VFD for old Myford ML8 wood lathe (0.5HP, single phase)

Thanks for the update.. and you just had a little taste of my world :)

PS - I'll be interested to know if that wire feeding the motor from their site pics is screened?.... if not it won't meet EU directives.

I'll post further pictures when it arrives (if it does this week) and again, I'll be grateful for any comments. :)
 
Another update... :)

Speed controller and new 1HP 3 phase motor arrived today.

lathe_speed_controller_box_exterior.jpg lathe_speed_controller_box_interior.jpg lathe_VFD.jpg lathe_speed_controller_box_door.jpg lathe_new_motor.jpg lathe_new_motor_connections.jpg lathe_with_speed_controller.jpg

I include the photos so that trainees can see things they might not have come across so far in their training, and also for mentors to comment/nod sagely/mock. ;)

In answer to Darkwood's question in post #13... no, the motor cable isn't screened.

:)
 
Last edited:
Oh dear ...Face PALM :38:..... I have rarely seen a panel so cheaply made plus it doesn't comply with European EMC directives the way its been built.. TBH it will work but you have purchased a non compliant poorly constructed and built bag of (well you can guess).... Check out page page 29 onwards for your model and just checkout the requirements for screening :)

https://www.inverterdrive.com/file/WEG-CFW-10-Manual

Its up to you if you fit and forget but me personally I'd be sending it back as a non-compliant to the LV directive and European EMC directive.... does it have a CE stamp all the wiring plans etc etc ?


PS you could unplug this control unit from the socket and receive a deadly shock of the plug pins ...I'm mortified!!!
 
Last edited by a moderator:
Oh dear ...Face PALM :38:..... I have rarely seen a panel so cheaply made plus it doesn't comply with European EMC directives the way its been built.. TBH it will work but you have purchased a non compliant poorly constructed and built bag of (well you can guess).... Check out page page 29 onwards for your model and just checkout the requirements for screening :)

I did notice that and chuckled...

shielding.png

https://www.inverterdrive.com/file/WEG-CFW-10-Manual

Its up to you if you fit and forget but me personally I'd be sending it back as a non-compliant to the LV directive and European EMC directive.... does it have a CE stamp all the wiring plans etc etc ?

CE stamp I'm not sure about (let's assume not). Wiring plans? Well, I've just taken some photos of the wires... I guess that counts, right? ;)
PS you could unplug this control unit from the socket and receive a deadly shock of the plug pins ...I'm mortified!!!

Well that's slightly terrifying. Are we talking, "whilst the motor's turning," or "motor off but switch on controller lid on" or "even if you switch off the DP switch"? Could you explain, please? :)
 
I did notice that and chuckled...

View attachment 29950



CE stamp I'm not sure about (let's assume not). Wiring plans? Well, I've just taken some photos of the wires... I guess that counts, right? ;)


Well that's slightly terrifying. Are we talking, "whilst the motor's turning," or "motor off but switch on controller lid on" or "even if you switch off the DP switch"? Could you explain, please? :)

With drives there is a requirement for isolation normally by use of a contactor that will automatically drop out if say an E-stop is hit (situation dependent) or more so a power failure due to the charged electronics within the drive which can take several minutes to discharge, all someone has to do here is leave that DP switch down and unplug it exposing the plug pins still in line with a charged Drive.

I can spot so many other breaches but its that one that stands out, the screening issue can see RF-interference locally and also harmonic issues in the mains.... I'm going to ask although your call if you want to divulge but how much did you pay for this?
 
Last edited by a moderator:
With drives there is a requirement for isolation normally by use of a contactor that will automatically drop out if say an E-stop is hit (situation dependent) or more so a power failure due to the charged electronics within the drive which can take several minutes to discharge, all someone has to do here is leave that DP switch down and unplug it exposing the plug pins still in line with a charged Drive.

Ah, right, see what you mean. Thanks.

I can spot so many other breaches but its that one that stands out, the screening issue can see RF-interference locally and also harmonic issues in the mains.... I'm going to ask although your call if you want to divulge but how much did you pay for this?

£400+VAT.
 
From the manual just to give you an idea of the breaches that may have been done here, I lack some info but some of it is obvious to me :shocked3:-

The CFW-10 inverter series was designed considering all safety andEMC (ElectroMagnetic Compatibility) aspects.The CFW-10 units do not have an intrinsic function until connected with other components (e. g. a motor). Therefore, the basic product isnot CE marked for compliance with the EMC Directive. The end usertakes personal responsibility for the EMC compliance of the whole installation. However, when installed according to the recommendations described in the product manual and including the recommended filters and EMC measures the CFW-10 fulfill all requirements of the (EMC Directive 89/336/EEC) as defined by theEN61800-3 "EMC Product Standard for Adjustable SpeedElectrical Power Drive Systems - specific standard for variable speed drives.The conformity of the complete CFW-10 series is based on tests performed on sample models. A Technical Construction File (TCF)was prepared, checked and approved by a Competent Body.

The following items are required in order to have an appropriated installation:
1) The motor cable shall be armored, or installed inside a metallicconduit or trunking with equivalent attenuation. Ground the screen/metallic conduit at both ends (inverter and motor). (poor wording here screened should be key word)
2) Control (I/O) and signal wiring shall be shielded or installed insidea metallic conduit ortrunking with equivalent attenuation.as possible.
3) The inverter and the external filter shall be closely mounted on acommon metallic back plate. Ensure a good electrical connectionbetween the inverter heatsink, the filter frame and the back plate.
4) The wiring between the filter and the inverter shall be kept as short.
5) The cable shield (motor and control) shall be solidly connected tothe common back plate, using metallic brackets.
6) Grounding shall be performed as recommended in this user’s guide.
7) Use short and thick cables to ground the external filter or inverter.When an external filter is used, ground only the filter (input) - theinverter ground connection is performed through the metallic backplate.
8) Ground the back plate using a braid, as short as possible. Flatconductors (e.g. braids or brackets) have lower impedance at highfrequencies.
9) Use cable glands whenever possible.
 
Last edited by a moderator: