I'd be interested to know what transpires if you can find the time to post again in a few days.
If ABB are prepared to swap out the drive at no cost then it would be wise to do so just to rule out that as a possibility.
If your pump is a multistage centrif then low head is not a place where you want to be, even if the head is slightly below specified minimum it can have a marked detrimental effect on mean time between failures so artificially introducing extra head pressure is a close second best to re-specifying a pump with a lower head requirement.
<1 second to >3450rpm is a steep start ramp, it's steeper than the default ramp settings of most drives so I'd double check these settings which may be critical to ensure bearing hydraulic action and possibly seating of the impellers. Also with bearings that rely on water hydraulics for lubrication I'd avoid dry run at all costs, it could lead to the demise of the pump faster than a marginally high run current.
Maybe consider a 0-10 volt level sensor (or something similar that's drive compatible) that can signal the drive to modulate the motor speed between 30-60HZ, it might be simpler and more reliable than PID operation.
Good luck and I'll look forward to reading what happens.
If ABB are prepared to swap out the drive at no cost then it would be wise to do so just to rule out that as a possibility.
If your pump is a multistage centrif then low head is not a place where you want to be, even if the head is slightly below specified minimum it can have a marked detrimental effect on mean time between failures so artificially introducing extra head pressure is a close second best to re-specifying a pump with a lower head requirement.
<1 second to >3450rpm is a steep start ramp, it's steeper than the default ramp settings of most drives so I'd double check these settings which may be critical to ensure bearing hydraulic action and possibly seating of the impellers. Also with bearings that rely on water hydraulics for lubrication I'd avoid dry run at all costs, it could lead to the demise of the pump faster than a marginally high run current.
Maybe consider a 0-10 volt level sensor (or something similar that's drive compatible) that can signal the drive to modulate the motor speed between 30-60HZ, it might be simpler and more reliable than PID operation.
Good luck and I'll look forward to reading what happens.