So earlier this year I obtained a large machine with a couple of 3 phase motors in it, and the rest single phase. I bought a VFD, correctly wired it up, and while the machine ran with some functions, it also reported "undervolt at source"
I had bought a VFD with a maximum output of 380 volts. Checking over the machine wiring, I found it had 415volt circuit breakers. However, the biggest draw from the 3 phase motor I found was .75amp. Perhaps I mistakenly believed the 380volt VFD would still run the machine.
So, does the "under volt at source" report on the VFD state I do not have 240volt at the source, or is the VFD indicating I need a higher voltage output VFD? The source is a 15 meter extension lead plugged into the house, the machine is in the shed. Would this distance be enough to lower the voltage at the shed end?
I found a higher rated VFD for sale locally, a 4kw, 6hp, 415volt. Would this be the solution?
Hopefully there are some knowledgable VFD people here?
Thanks, Gareth
I had bought a VFD with a maximum output of 380 volts. Checking over the machine wiring, I found it had 415volt circuit breakers. However, the biggest draw from the 3 phase motor I found was .75amp. Perhaps I mistakenly believed the 380volt VFD would still run the machine.
So, does the "under volt at source" report on the VFD state I do not have 240volt at the source, or is the VFD indicating I need a higher voltage output VFD? The source is a 15 meter extension lead plugged into the house, the machine is in the shed. Would this distance be enough to lower the voltage at the shed end?