Found this today (circa 1958)....must have been tedious “clacking” these out on a type writer back in the day!

[ElectriciansForums.net] Vintage Fuseboard Schedule
 
could one of the older guys enlighten me as to what size roughly in metric 19.052 is and also 7.029
Hmm, I wonder whether I'm supposed to count myself in that category or not?

For the benefit of the younger guys, those cables sizes are not quite written correctly on the schedule; they should be 7/.029 and 19/.052, meaning seven strands of 0.029 inches diameter etc. The quickest way to convert to metric is to multiply 507 by the number of strands and by the square of the diameter.

507 x 7 x (0.029)² = 3.0mm²
507 x 19 x (0.052)² = 26mm²

Also, guys of all ages, we need stuff like this for the museum. Anyone finding old paperwork from electrical contractors, drawings, schedules, invoices etc please let me know if you don't want it.
 
Hmm, I wonder whether I'm supposed to count myself in that category or not?

For the benefit of the younger guys, those cables sizes are not quite written correctly on the schedule; they should be 7/.029 and 19/.052, meaning seven strands of 0.029 inches diameter etc. The quickest way to convert to metric is to multiply 507 by the number of strands and by the square of the diameter.

507 x 7 x (0.029)² = 3.0mm²
507 x 19 x (0.052)² = 26mm²

Also, guys of all ages, we need stuff like this for the museum. Anyone finding old paperwork from electrical contractors, drawings, schedules, invoices etc please let me know if you don't want it.
If you PM me an address and I’ll post it out to you.....I’ve got a few stamps.
 
Fantastic! Thank you, address follows. I think we've got a fuseboard with Grierson's label on the front but not 12-way unfortunately, so we can't pretend the schedule goes with it.
 
Fantastic! Thank you, address follows. I think we've got a fuseboard with Grierson's label on the front but not 12-way unfortunately, so we can't pretend the schedule goes with it.
How many ways is it? I might come across some more.
 

Reply to Vintage Fuseboard Schedule in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Not sure if they were unique but they did not incorporate a thermal trip it was all magnetic.
Replies
6
Views
514
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
671

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top