OP
jackofall
This is getting a little confusing - where can you buy VOELCBs in the UK today?
Is there a specific reason why one is used rather than a standard 30ma RCD?
No decent Designer would specify a VOELCB without good reason, as it is clearly not compliant with the Wiring Regs for a new installation.
The VOELCB may well give a sufficient additional protection, but, it cannot be verified unless you have the specialist equipment to do that, even then,it will not comply with the Regs, and in my view, will not comply with one of more of the vehicle supply regulations, as the electrical install in it cannot be proven to be safe.
There are a couple of reasons that have been quoted to me for this setup. The first one, that it was stipulated on the original requirements, and as I have mentioned before, I think this should have been kicked into touch then. The next, they cant use and RCD due to the amount of earth leakage within the platform, which to me indicates bad design as you can always sort that out during the design stage even if you have to go to the extreme of rectifiers and invertors with the ccts split up etc. That could have had its own advantage of beefing up the UPS system as well.
But as to where you can buy them, you got me there, as not on the procurement side of life.