is this right

mv on chosen cable from regs x length of cable run x design current of circuit

divided by 1000

is it calulated amps or the breaer your going to use

is that all as im trying to work out for this lighting circuit but to get the volt drop under 3% the cable needs to be 6mm


ta for help
 
Then 6mm sounds about right.
Using a certain suppliers online calculator -

3kw lighting circuit over 60m, clipped direct =

Required Cable Size6 mm
Voltage Drop5.71 Volts.
Percentage Drop2.5%
Current Load13.0 Amps
Max Cable Load[SUP]*[/SUP]47.0 Amps
 
yup thats how i worked it out from my regs and a calc

but when i went onto an online calc it said 2.5 was fine which confused me

not really possible to shorten run as its the switch wire which is causing the problem only option is to make into 2 circuits or just use 2 lights

have my calcs been right though
 
If this circuit is longish then to get an accurate VD figure you need to calculate at each lamp, something similar to calculating VD and cable sizing on street lighting!!

Remember the first lamp position on the circuit will have the shortest distance, but the largest load, while the last lamp will have the longest distance but the least load...
 
If this circuit is longish then to get an accurate VD figure you need to calculate at each lamp, something similar to calculating VD and cable sizing on street lighting!!

Remember the first lamp position on the circuit will have the shortest distance, but the largest load, while the last lamp will have the longest distance but the least load...

What Engineer said is correct.

Let's say your 4 x 400W lights are spaced equally along the 60m run, 1 every 15m

Assuming 230V supply and 2.5mm² clipped direct...


a) The cable from DB to light 1 will carry the full load current
I = 1600 Ă· 230 = 6.96A
VD =
(18 x 6.96 x 15) Ă· 1000 = 1.88V

b) The cable from light 1 to light 2 will carry Âľ of the load
I = 1200 Ă· (230 - 1.88) = 5.26A
VD = (18 x 5.26 x 15) Ă· 1000 = 1.42V

c) The cable from light 2 to light 3 will carry ½ the load
I = 800 Ă· (230 - 1.88 - 1.42) = 3.53A
VD =
(18 x 3.53 x 15) Ă· 1000 = 0.95V

d) The cable from light 3 to light 4 will carry ÂĽ of the load
I = 400 Ă· (230 - 1.88 - 1.42 - 0.95) = 1.77A
VD = (18 x 1.77 x 15) Ă· 1000 = 0.48V


Total VD = 4.73V (2.06%)


As you can see you are well under the 3%.
 
Last edited by a moderator:
Would you calculate like this for a ring final circuit, work out at 5% between each socket etc?

No. This is for "distributed loads" where you know what the load will be at each point in the circuit.

Ring circuits are calculated normally and the result divided by 4 i.e ((mV/A/m) x Ib x L) Ă· 4, L being the total length of the ring from end to end.

The design current of a 32A ring is taken as 26A, 20A at the mid-point of the ring and the remaining 12A shared between each leg (6A each leg), therefore no point in the ring should carry more than 26A if you get what I mean.

So the volt drop in a 50m ring circuit wired in 2.5mm² would be calculated like this:

((18 Ă· 1000) x 26 x 50) Ă· 4 = 5.85V (2.54%)
 

Reply to volt drop calc in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

Similar threads

Thanks little spark. Good point but the drivers I'm considering have a sync and communication between driver function. So (as long as it works)...
Replies
6
Views
590
I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
696

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top