Has anyone ever had a volt drop issue?

Just for fun.......... yes i said fun, i cant believe i would be saying that in my mid 20s

But i did a calc for a radial circuit in in swa

B32 mcb
4.0mm 3core swa
35m run

(mV/A/m)

So...... 11X32X30/1000 = 10.56

Way over the 5% in table 4Ab

Am i missing something? Would the design current me lower as there is no way the circuit would pull 32a
 
One of the dangers of a building site is the impedance of cables plugged into yellow bricks. With proper transformers there is no problem as the MCB's are fitted to the output, but the yellow brick often has a 10 or 12 amp overload on the incomer only, so at 55 volt to earth 10 x 230 = 2300 VA / 55 = 42 amp, and 1.5 mm yellow flex will not take 42 amp for long. With a single cable the resistance of the cable is low enough that is a scaffold pole falls and causes a line - earth fault more than 42 amp flows so the trip operates, but once you start plugging cables into cables you can't get the 42 amp needed to trip the overload.

I personally think the dangers of fire exceed the danger from electric shocks and a risk assessment would show better to use 230 volt now nearly every supply is RCD protected, so on a site not large enough for a proper 110 volt supply using 230 volt is safer.

I can't see how the yellow bricks comply, but it seems they are still used.
 

Reply to Volt drop in the real world in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Well another week passed and I still don't have a proper answer to where the process is wrong. To reiterate, this is not a question for a real...
Replies
2
Views
126
  • Question
As you have actually measured the cold resistance (R1 + Rn = 0.15) then you have the voltage drop at the expected current (60A) so you can compute...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top