So the scenario. I’ve been asked to design this for a friend, who is the one signing it off. I know its on his call. But also I know that bad habits creep into peoples work. So I would appreciate what you guys say as well.
Here’s what I am doing anyway.
- Update home consumer unit and move to garage
- Install DB in spa and associated cabling & garden lighting
- Install but not connect cable for future annex at bottom of garden
1) Update home consumer unit.
Currently a 6 way re-wireable fuse board with 3 x 30 amp powering 2 rings (1 with an unknown spur) and presumably the cooker, and 2 x 5 amp seemingly powering 3 lighting circuits.
Board is located in the meter box.
New CU to be placed on inside of wall and across into garage about 2m from current position
Henley block tails coming from meter and run extension tails to new board.
The new CU will be an 8 way board for spare capacity. Circuits replaced respectively with RCBO’s (3 x 32 amp, 1 x 20amp & 2 x 6 amp) And 63amp MCB type B for distribution to DBs.
2) Install Spa DB and cabling. Spa wood built
SPA power requirements:
Estimate 40 Amps
Hot tub. Standard requirement 32 amp radial
Sockets. radial 16 amp protection.
Lights. A few LED internal & external lights. 10 max @ 50W = 2.2amp. 6 amp protection
Garden lights. 20 LED all around the garden at regular intervals. @ 50W = 4.3 amp. 6 amp protection
Spa DB to be 4 way board with RCBO’s. DP 60 amp isolator
Cable to run from 63amp MCB at CU, underground to Henley block on the spa building. (Henley block on spa for future power to lower annex.
Hot tub will run from RCBO TYPE C to 45 amp isolator, to hot tub position
Garden lights will run around whole garden in SWA with lights approx. every 2 meters. The SWA will come up to a wiska box and the light will take power from that
3) Annex. Brick built with wiring in walls
Estimate 20 amps
Annex power requirement:
Potential for shower/water heater max 5kw
Sockets 16 amp
Lighting, A few LED lights both internal and external.
Building will not be built until next year.
Supply cable for distribution.
Run underground to spa into Henley block, then (disconnected for time being) underground to annex.
House is currently PME. No extraneous parts in either building so no need for TT
Volt drop calculated by taking mV/A/m x Ib x length / 1000 then divide by 2 as load isn’t at the end.
Cable spec:
Distribution,
16mm SWA, 25m to spa, 25m to annex. 50m total. Capacity= 91amp Volt drop = 1.6V at halfway, 3.2V to annex
Garden lights
1.5mm SWA, 65 m around garden from spa. Capacity= 25 amps Volt drop = 4V
Other cable as standard