Hi I have a query one of you may know the answer to. I have installed some lights in the woodlands for a customer and he is using 12watt LED lights he is only installing a few i think it was 186 watts or something. I have used SWA cable 1.5 mm as it is about 200metres and worked out the voltdrop. He now wants to extend it another 100m and add on a few more lights!! I have told the customer that it will incur too much volt drop as the resistance on the cable.

For my own sake was wandering the dangers of volt drop obviously appliances wouldnt work correctly as the volt drop and the resistance is high so surely it cant do the cable any good.

Was wandering what you guys would do and if you have any past experiences or knowledge.

Thanks
 
You work from the 220V source to the first fitting to give 220V-Vd1 as the voltage at the 1[SUP]st[/SUP] fitting. On to the second fitting where (220V-Vd1)-Vd2=voltage at the second fitting. At the third fitting the voltage is ((220V-Vd1)-Vd2)-Vd3 and so on. The volt drop gets exponentially smaller with each step due to the progressive reduction in voltage and current along the line. The end result is towards the end of the line voltage drop is reduced as is the current.

If any of you are in to doing excel spreadsheets it’s a fantastic maths problem!

(**** I’ve started something now, this is going to take some time)
 
You work from the 220V source to the first fitting to give 220V-Vd1 as the voltage at the 1[SUP]st[/SUP] fitting. On to the second fitting where (220V-Vd1)-Vd2=voltage at the second fitting. At the third fitting the voltage is ((220V-Vd1)-Vd2)-Vd3 and so on. The volt drop gets exponentially smaller with each step due to the progressive reduction in voltage and current along the line. The end result is towards the end of the line voltage drop is reduced as is the current.

If any of you are in to doing excel spreadsheets it’s a fantastic maths problem!

(**** I’ve started something now, this is going to take some time)

Already done 1 a while back

[ElectriciansForums.net] Volt Drop
 
All this talk about volt drop.

Has anybody considered the circuit impedance with regards to disconnecting the circuit in the event of a short circuit.

The R1 + Rn of 200m is 4.84Ω and would be OK.

However, 300m would push it up to 7.26Ω and that is before taking into account the impedance of the supply cables and transformer winding.

As the maximum measured loop impedance (using the 80% rule of thumb) for a 6A Type B breaker should be 6.18Ω you would already be over.

You can get away with 1667Ω for the EFLI by using an RCD but that won't work for short circuit as we all know.

Just a thought.
 
Last edited by a moderator:
All this talk about volt drop.

Has anybody considered the circuit impedance with regards to disconnecting the circuit in the event of a short circuit.

The R1 + Rn of 200m is 4.84Ω and would be OK.

However, 300m would push it up to 7.26Ω and that is before taking into account the impedance of the supply cables and transformer winding.

As the maximum measured loop impedance (using the 80% rule of thumb) for a 6A Type B breaker should be 6.18Ω you would already be over.

You can get away with 1667Ω for the EFLI by using an RCD but that won't work for short circuit as we all know.

Just a thought.

Very good point.
That's probably why it should be a ring or the extra 100m run as a separate circuit.
I did a basic Volt drop calculation on the same idea as yours but using 4 1A loads at 10m intervals with a theoretical volt drop of 10mV/A/m and found that the basic calc (end of line * total load) gave a VD of 1.6V and doing successive addition of volt drops with diminishing loads gave a VD of 2V .
Not that it makes much difference since you have already proved the potential addition to the circuit has flawed.
 
What would the volt drop calc be if it was converted to a ring - use total load and effectively quarter the distance?

Using my example you would need to increase the end load by one length so that you could get back to the supply.
The mV/m/A would now be 1/2 but the load would stay the same but with less effective outlets (paralleled) giving a total VD of 0.45V which is approximately 1/4 of the difference of 2V and 1.6V.
 

Reply to Volt Drop in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top