Hi and welcome.

Firstly 4.5V sounds very high for 12m of 1.5mm. You've maybe made an error there.

You can calculate the length of the ring final by measuring r1 or r2 (end to end of live or the cpc). You can then calculate the cable length by finding the ohms per metre for the cable size that's been installed.

Brill thanks, darkwood would you calculate like impeededloop wood?
 
This has been covered many times and should be in your OSG - but here's a link to a better explanation and shown calculations..

http://www.electriciansforums.co.uk...istribution-load-ring-final-voltage-drop.html

Been a domestic property I'm assuming the ring is connected to the origin of the supply, if by chance its a submain remote from the origin then you have to also calculate the VD for the Sub-main too.... if their is any lighting on the submain then this would mean that the submain will have to comply to the lower VD% for lighting circuits....

Not really a issue in domestic but when you have submains then things get interesting.
 
sorry but your calc is flawed.

firstly extend the ring with fcu for lighting, you wont hit 100m total length for ring.

you should only have the lighting off the fcu


cheating method is zs on socket you are going to extend the ring from to see if zs is low enough, extend then test properly
 
sorry but your calc is flawed.

firstly extend the ring with fcu for lighting, you wont hit 100m total length for ring.

you should only have the lighting off the fcu


cheating method is zs on socket you are going to extend the ring from to see if zs is low enough, extend then test properly

I don't think the OP's intended method is incorrect. He's quite rightly trying to design his circuit first to check it will comply with 7671.
 
18x26x66%1000=30.888 volt drop for a ring circuit, ??

mV x amp x meters%1000 is my calc have i missed something here?? As obviously its not right
 
.........
fb4bfb8f90f56b6f5ec243df376d8e8b.jpg
 
I know a ring main dosnt need calc if a new installation as long as it served no more than 100sqm but if your calc it for a fcu of 13amp for a radial circuit for 1.5mm for 12m how would you calc it to add to the calc for the spur, as obviosly this is above 11.5v drop?
 

Reply to Volt drop in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
732
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
972

Similar threads

  • Question
Well another week passed and I still don't have a proper answer to where the process is wrong. To reiterate, this is not a question for a real...
Replies
2
Views
250
Good question now to start with thermosetting insulated conductors are not tri-rated that is something different. Table 4E1A deals with this type...
Replies
1
Views
280

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top