Evening people
At it says getting about 90v at
fitting between l-n & l-e with sw off What could be causing this all tests ok . Ir around 250 l-e & 300 l-n .
Ta
 
A lot of induced voltage. Try isolating all circuits then bring them on one at a time whilst monitoring the voltage, this should give you a rough idea of where to start.
 
Someone's probably dumped an extra 20 feet of T+E under the boards and got the cables all twisted up, great for magnetising screwdrivers!!!
 
Cheers strima its only when lighting circuit is on everything else off . Found it last thing today ill investigate more monday.

This appears to be at odds with your #1 post ... do you actually mean lighting circuit OFF and everything else ON perhaps? Also what instrument are using to measure the voltage?
 
Markiesparkie
All other circuits off . Lighting circuit on switch to light fitting off voltage between switch return and neutral or earth at fitting approx 90v. Measure with megger mft 1720.
 
As a thought check the connections - I had this on a socket the other week - the terminal was lose giving me 120v L-N, 240v L-E and 120v N-E.
The terminal was lose creating a large resistance between the neutral terminal and cable.
 
Just thinking is this a 2 way light switch? - there for this should not have any voltage on the side not being used.

Do a IR test between both switched Line terminals of the switch (with the cables attached) - someone might have put a nail through it or a fried mouse
 

Reply to voltage at light fitting switch off in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
783
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

Induced voltage can be a bit of a red herring when using DVM my guess is somethings moist.
Replies
5
Views
422
T
  • Question
What @Avo Mk8 suggests crossed my mind. Try an IR test at 500v.
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top