At it says getting about 90v at
fitting between l-n & l-e with sw off What could be causing this all tests ok . Ir around 250 l-e & 300 l-n .
Ta
 
No truckster havent . How would that tell you.
Ta

A Loz voltage tester puts a low impedance as opposed to the nomal high impedance across the contact points which allows the induced current to drain so you get a more accurate measurement. I had a leaflet on it somewhere but can't find it. I think I got it from the Fluke website so you could have a look there.
 
Last edited:
Agree with truckster, are the switch wire and the feed in the same cable. To understand it a bit better, get a couple of metres of twin and earth connect the live and earth in a plug top leave the blue disconnected out of the plug and terminate the wires at the other end in block connectors, when the brown is live there will be a induced voltage on the floating wire(blue) it can't go anywhere until there is a bulb or resistor for it to flow to 0volts.
 

Reply to voltage at light fitting switch off in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

Induced voltage can be a bit of a red herring when using DVM my guess is somethings moist.
Replies
5
Views
425
T
  • Question
What @Avo Mk8 suggests crossed my mind. Try an IR test at 500v.
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top