Sting Ray

After installing some LED fittings in a bathroom and disabling an electric shower circuit I carried out a check on the whole installation. All fine until I used my Di-LOG probe to probe the switch plate screws to check that I had not pinched any live wires in the light switch back boxes around the house (not sure what made me do that?). One switch lit up the voltage present light so off it came. No trapped wires but using my Megger MFT1730 I see around 20 volts between the earthed back box and the switched line when the switch is open, 244V when closed. Disconnected the cable from the ceiling rose and the switch and carried out insulation tests between all conductors, everything >999M. Re-connected and the 20 volts was back.

Does anyone know what I'm seeing/experienced this before and is it real? Or should I just not be so inquisitive!
 
probably induced voltage. try using an analogue voltmeter. it'll probably disappear. was the switch in question 2 way?
 
any cables running in proximity of your switch cable. as i said before. try an analogue meter. the lower input impedance will drain away any stray voltage.you may see an initial "kick" of the needle should then settle at 0V".
 
Definately sounds like induced to me,thats the problem with using DMM,s many years ago I had a fault on a car and was convinced it was the fuel pump,the fluke meter said 12v going to pump but pump not running,anyway the AA man who came out wasn't convinced and tested using a bulb on 2 bits of wire,guess what no power.Turned out it was a duff relay under the dash.DMM's have their place but sometimes you just need that extra bit of load.
 
Am I being dopey or did the OP say that back box is supposed to be earthed? If it is, then induced voltage(from PL to SL) would explain a reading with the switch off, as the LED driver wouldn't be guaranteed to present a near-zero forward voltage L-N like a filament lamp. But it doesn't explain the original presence of voltage on the screws, which points to a disconnected CPC. There could still be enough leakage for the MFT to read 240V L-CPC with the switch on.

What was the Zs at the switch?
 
Am I being dopey or did the OP say that back box is supposed to be earthed? If it is, then induced voltage(from PL to SL) would explain a reading with the switch off, as the LED driver wouldn't be guaranteed to present a near-zero forward voltage L-N like a filament lamp. But it doesn't explain the original presence of voltage on the screws, which points to a disconnected CPC. There could still be enough leakage for the MFT to read 240V L-CPC with the switch on.

What was the Zs at the switch?
Depends,he said he'd initially used a DiLog test lamp,now if its the same one I had they do automatic continuity test,so maybe it was the continuity light that was on,reading through neutral to earth? Just another possibility to throw into the mix.
 
But he did that first test to the screw with the switch in place, so he would not have had access to anything but the CPC, which should never light an indicator. We need to know what that test actually was.
 
Zs at the switch and the outlet is 0.61, Ze 0.2, giving an approximate cable length of 13.5m which is about right as this room is directly above the main board
 
I know I can buy this via the web but thought I'd try some of my local distributors (Edmundsons, Senate, CEF) yesterday. No one had heard of this item let alone stocked it although they were all keen to show me fine collections of hen's teeth and rocking horse ****! "What's an analogue voltmeter?" one said LOL.
 
Incidentally, whilst re-testing the switch again yesterday with the DiLOG, sometimes the voltage indicator (forked lightening symbol) didn't light up but would always do so if I touched any wall. Temperature yesterday was 31C! and all the walls in the house are of dry lining construction.
 

Reply to Voltage between earth and switched line terminal on one way light switch in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

Good point but then regular plastic switches aren't permanently running a wireless network module inside. It just seems odd not to have an earth...
Replies
2
Views
1K
Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
479

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top