S
s100cky
Hello All!
I was hoping to have some help from some of the savvy bunch if at all possible? I am currently pricing a largish job for a client of mine. It involves changing some warehouse lighting (currently fluourcesents to 400W metal halide low bays. The warehouse is 75 meters long, and 50meters wide (remember this it will be useful later!)
So I thought id blow the dust of my IEE electrical installation design guide (as I havnt really looked at this since college), and started playing around with some calculations…
8 lights x (400w x 1.8) = 5760W/230 = 25.04 (brilliant that’s my design current sorted!)
Now to find a cable size! Im running in some lighting trunking, we will say less then 40% full! Ill start with a 4mm PVC single. (why not?!) and start playing with volt drop..
Table 4D1B tells me volt drop = 11 so…
11x100(75m warehouse plus 25m to the centre of the warehouse) x 25A / 1000 = 27V volt drop!!
Ok a 4mm is no good, lets try a 10mm..
4.4x100x25 / 1000 = 11v (219V end of circuit)
Well that seems to just about comply, but do I really have to use a 10mm single core for this circuit? I know all my calculations are at face value, but am I missing something vital, just doesn’t seem to make sense.
Like I said this is a largish job for me, and I want to make sure im covered on all angles, any useful input would be really helpfully.
I was hoping to have some help from some of the savvy bunch if at all possible? I am currently pricing a largish job for a client of mine. It involves changing some warehouse lighting (currently fluourcesents to 400W metal halide low bays. The warehouse is 75 meters long, and 50meters wide (remember this it will be useful later!)
So I thought id blow the dust of my IEE electrical installation design guide (as I havnt really looked at this since college), and started playing around with some calculations…
8 lights x (400w x 1.8) = 5760W/230 = 25.04 (brilliant that’s my design current sorted!)
Now to find a cable size! Im running in some lighting trunking, we will say less then 40% full! Ill start with a 4mm PVC single. (why not?!) and start playing with volt drop..
Table 4D1B tells me volt drop = 11 so…
11x100(75m warehouse plus 25m to the centre of the warehouse) x 25A / 1000 = 27V volt drop!!
Ok a 4mm is no good, lets try a 10mm..
4.4x100x25 / 1000 = 11v (219V end of circuit)
Well that seems to just about comply, but do I really have to use a 10mm single core for this circuit? I know all my calculations are at face value, but am I missing something vital, just doesn’t seem to make sense.
Like I said this is a largish job for me, and I want to make sure im covered on all angles, any useful input would be really helpfully.