Currently working on a job where the client was concerned about the swimming pool heat pump tripping the mcb (the mcb is more than adequate for the job).
The heat pump 4kw and pool pump 1.2kw were drawing 27/28 amps with only 197 volts measured at the pump room. It’s about a 60 meter run.
I replaced the 6mm cable run with 10 mm and the figures are still very much the same - I expected the voltage drop to be much less and therefore the amps to come right down, but no.
Any thoughts??
 
The main panel voltages are given in post #6. L3, serving the heat pump, is low at 218V, but that is a separate issue to the unaccountable drop in the heat pump circuit.
 
Further thoughts:

It is a swimming pool heat pump so I'd expect long periods of running.

Maybe:

1. Bearings are failing/have failed in compressor or its motor or both.
2. Low lub oil level in compressor.
3. High pressure fault in refrigerant circuit not detected by faulty HP pressure sensor.

All would cause comp motor to work harder and draw more current.
 
The main panel voltages are given in post #6. L3, serving the heat pump, is low at 218V, but that is a separate issue to the unaccountable drop in the heat pump circuit.

It doesn't seem clear to me whether the OP has measured that incoming voltage with the heat pump running or not.
My thoughts at the moment are that if the incoming voltage is dropping to, or near to, 197V when the heat pump is running then that will be relevant.
 
Re my #18: I forgot to add a fourth:

4. Check that water flow through the condenser ( an heat exchanger) - which transfers the heat of the hot pressurised refrigerant vapour to the circulating pool water - is not restricted or throttled by defective valves or valves not fully open. Also check that the pool pump is running at its correct speed and the pump is not restricted - is there a strainer which needs clearing/replacing? If the volumetric flow of the pool water is lower than it should be, the refrigerant in the condenser will be at a higher temperature than it is designed to be at which means a higher back pressure at the compressor outlet. The compressor will have to work harder - more amps - to pump the refrigerant into the condenser.
 
Last edited:
Don't forget starting current which may be 5 times higher on a conventional motor. The manufacturer might specify a maximum cable resistance that allows reliable starting at a certain head pressure at minimum supply volts.
 

Reply to Voltage drop problem not resolved with bigger cable in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
259
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
749
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
738

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top