Why all the complicated formulea for working out voltage drop?
Why not just connect the load and measure the voltage with a meter?:confused:

So what happens when you have installed the new circuit etc etc infront of the customer and then when you connect the load find the voltage drop is to much so infornt of the customer you have to remove the incorrect cable and put in the next size up just to find out thats wrong as well. Need I say more.


Chris
 
So what happens when you have installed the new circuit etc etc infront of the customer and then when you connect the load find the voltage drop is to much so infornt of the customer you have to remove the incorrect cable and put in the next size up just to find out thats wrong as well. Need I say more.


Chris


:eek::eek::eek::eek::eek::eek::eek::eek:


oops......

I Blame the beer..............
 
Sorry for raking it up again but it's interesting. Table 7.1(1) latest OSG gives a maximum length of cable as 59m for 1.0mm with ref method 101 on a type B 6a mcb. Table F6 OSG gives ccc of 1.0mm with ref meth 101 of 10.5a and vd of 44mV/A/m. But the cable length permitted doesn't work out if you calculate the vd with an Ib of 6a and cable length of 59m. 44 x 6 x 59 / 1000 = 15.58v which is way in excess of 6.9v (3%). Or have I picked this up all wrong?
 
Cheers Tony, it's a hypothetical question thankfully. What I was trying to fathom out was why OSG reckons you can have a 59m cable run on a 6 amp breaker installed with 1.0mm with ref meth 101. How do you interpret the tables?

Rob
 
Mind you I've done an install/alteration recently whereby an R1+R2 value on a landing light measured 1.59 which indicates a cable run in the region of 43m on a circuit with a design current of 4.4a (diversity taken into account). There was no way it was 43m long. 30m max. The value didn't drop significantly after a circuit 'tightening' up exercise either and the tester is fine...
 
Hi Rob, I dont think the values in the table have been calculated using 6amp as the design current or lighting load. It also will take into account that the lighting load will be spread along the full length of the circuit evenly and not all at the far end.
 
Forgive me Jonny, could you clarify further for me? Am I confusing the purpose of the two tables as they appear to conflict. If I calc correctly you could only have a load of around 2.5a on a 59 m cable run on 1.0mm on ref meth 101? Sure I'm calculating incorrectly somewhere. Cold you review the string from where I came in if you have the time. Cheeky I know!
 

Reply to Voltage Drop in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

The cable is way undersized. If the voltage drop is detrimental to the installation I would make a mention of it as volt drop generally is not...
Replies
2
Views
274
Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Replies
14
Views
653

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top