Bern1e

Hi folks!
Any answers on this problem?
I attended site and was told various items of equipment caused the rcd to trip randomly,after checking the Ze and voltage I tested the rcd which wouldn't trip x1 or x5.
I then deemed this faulty and replaced the rcd only to find this also did not trip.
I then decided my tester might not be working so i used another and the same problem occurred,by this point I am pulling my hair out.
After testing the supply voltage I noticed that when more appliances were plugged in the voltage decreased.
It was also noted the rcd would test on the incoming supply cables end but not the busbar side.
I m now deciding t become a brick layer !!!!!!!!
Help please me thinks uk power networks problem and loose neutral there endis the issue.
 
Ensure when you are running your bricks you have set a guide line up to keep your run level, use a good cement mixture and don't rush it until you have gained the expertise of a well seasoned brickie... hope that helps ;)
 
Was this site in a rural location possibly at or near the end of an overhead supply , I have seen a very similar situation where I live especially when off peak supplies are switched in. if this is what your finding then yes its UK power networks issue , what is the lowest reading your getting ...
 
Maybe also measure a neutral-earth voltage when it's under load and the voltage drops and take your measurements at the first available point in the premises. This might help indicate a supplier neutral issue.
 

Reply to Voltage dropping in a domestic house as you use more appliances ? in the Domestic Electrician Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
644

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
974
I fitted a Mem MR30 Pod and MCB, about ÂŁ75 for both.
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top