Hi folks!
Any answers on this problem?
I attended site and was told various items of equipment caused the rcd to trip randomly,after checking the Ze and voltage I tested the rcd which wouldn't trip x1 or x5.
I then deemed this faulty and replaced the rcd only to find this also did not trip.
I then decided my tester might not be working so i used another and the same problem occurred,by this point I am pulling my hair out.
After testing the supply voltage I noticed that when more appliances were plugged in the voltage decreased.
It was also noted the rcd would test on the incoming supply cables end but not the busbar side.
I m now deciding t become a brick layer !!!!!!!!
Help please me thinks uk power networks problem and loose neutral there endis the issue.