Hi,
I`ve been to a site today and noticed some units I`ve got have huge voltage drops. Voltage was fluctuating between 170V and 280V and on some units, I`ve had 330V.
I went to the DB board:
It looks like the issues is on the floor and feedback this on the DB board.
There are about 15 circuits. Each of them is connected to two spurs and feeding some VAVs boxes.
What could be the reason of the voltage fluctuating like this?
Many thanks,
I`ve been to a site today and noticed some units I`ve got have huge voltage drops. Voltage was fluctuating between 170V and 280V and on some units, I`ve had 330V.
I went to the DB board:
- Between live and earth some circuits were showing 217V and other one were showing 270V.
- Between Neutral and Earth, some circuits were showing 60V. When isolating each all MCBs, I`ve had 240v between neutral and Earth.
- The main supply was ok.
It looks like the issues is on the floor and feedback this on the DB board.
There are about 15 circuits. Each of them is connected to two spurs and feeding some VAVs boxes.
What could be the reason of the voltage fluctuating like this?
Many thanks,