Hi everyone,
Hopefully someone can help me with this?!
I am in the throws of finishing a domestic rewire in an empty house this week and yesterday was re-sleeving some CPC's in pendant light fitting that my apprentice had sleeved poorly.
Rather naughtily I was doing this while the pendant was live, but as the house was empty and the CPCs would only be disconnected momentarily I saw no real danger.
Having said that... during the disconnection and 'de-sleeving' of the CPC's I noticed a rather slight shock sensation when I touched the switch cable CPC and either of mains loop CPC's simaeltaneously? (It should be noted that the lighting circuit is wired in the traditional mains loop and single switch cable method).
On closer inspection and measurement using my multi-meter I found 190 volts between the switch cable CPC !
I investigated further and found the same voltage between the switch cable CPC & neutral but only usual small residual voltage between both mains loop CPC's and neutral.
Out of curiosity I disconnected the switch cable live, switch live and CPC both ends, I.R tested it at 500V DC only to get clear results @ >200 Ohms across the board.
Hoping I had cleared the 'fault' in the process described above I put everything back to together again, re-energised the the circuit and re-tested my CPC's and as before I had 190 Volts on the switch cable CPC!?
It should be noted that the switch back-box in question, although a metal back-box, is mounted on a wooden stud in a wooden stud partition so I don't think their could be any parallel paths or differing earth potentials as a result generating this potential difference.
The only thing I can think is that the switch is a dimmer and maybe there is some kind of induced voltage at play from the inductivity of the dimmer interacting with the metal back-box, but that really is clutching at straws!
Help Please!
Hopefully someone can help me with this?!
I am in the throws of finishing a domestic rewire in an empty house this week and yesterday was re-sleeving some CPC's in pendant light fitting that my apprentice had sleeved poorly.
Rather naughtily I was doing this while the pendant was live, but as the house was empty and the CPCs would only be disconnected momentarily I saw no real danger.
Having said that... during the disconnection and 'de-sleeving' of the CPC's I noticed a rather slight shock sensation when I touched the switch cable CPC and either of mains loop CPC's simaeltaneously? (It should be noted that the lighting circuit is wired in the traditional mains loop and single switch cable method).
On closer inspection and measurement using my multi-meter I found 190 volts between the switch cable CPC !
I investigated further and found the same voltage between the switch cable CPC & neutral but only usual small residual voltage between both mains loop CPC's and neutral.
Out of curiosity I disconnected the switch cable live, switch live and CPC both ends, I.R tested it at 500V DC only to get clear results @ >200 Ohms across the board.
Hoping I had cleared the 'fault' in the process described above I put everything back to together again, re-energised the the circuit and re-tested my CPC's and as before I had 190 Volts on the switch cable CPC!?
It should be noted that the switch back-box in question, although a metal back-box, is mounted on a wooden stud in a wooden stud partition so I don't think their could be any parallel paths or differing earth potentials as a result generating this potential difference.
The only thing I can think is that the switch is a dimmer and maybe there is some kind of induced voltage at play from the inductivity of the dimmer interacting with the metal back-box, but that really is clutching at straws!
Help Please!