Hello all, be gentle I am newly qualified and this is my first post! I have a customer who cannot get their boiler serviced due to a 5 volt current on their gas pipe when the upstairs lighting circuit is energised. All the supplemental and equipotential bonding seems ok, tests are within limits when the circuit isn't energised. There are a few issues with labelling on the CU but other than that all seems to check out OK. Is my best way forward to get at all the wiring and check for some sort of contact here? No obvious contact in visible places and the pipes are not showing any voltage downstairs. Can only assume that somewhere the lighting circuit is 'leaking' somewhere. Any advice on how some of you guys would proceed would be most welcome!
 
I've moved most of the visible wires away. There's one area where some lighting wiring shares an entry point with pipe work and has been plugged with expanding foam, I'm guessing that's a possible hot spot !!

Some expanding foams (and Gripfill) have an adverse reaction with PVC cable insulation causing it to breakdown.
I had a situation a few years ago where an outgoing lighting cable shared an access hole with the incoming overhead supply cables. This hole had been filled with expanding foam causing breakdown of the cable insulation allowing leakage from the incoming line to power the lighting circuit. The first indication of the problem was when the switch cable was about to be cut to length and the cutter blades switched the lights ON even though the installation was "safely isolated" at the DB main switch.
 
I would be tempted to use the volt stick he left,, and start splitting the circuit up till the stick goes out,,, it may point you in the right area... split what you think is thge middle does it still light and work from there..
 
I have one too and can confirm that it's quite insensitive to phantom voltage, but it's not infallible.

No mate: I know it's not infallible but compared to most of them it's pretty good, my first one got stood on by some lump of a Builder & the only 1 I could get quickly was a Di log. Damned thing would show the air was live, took it back & they gave me some other make & that picked up ghost voltages all over the shop. so went & bought another MK & am sticking with them.
 
I would be tempted to use the volt stick he left,, and start splitting the circuit up till the stick goes out,,, it may point you in the right area... split what you think is thge middle does it still light and work from there..

Been wondering about that, what sort of Gas fitter gives up his good working tester to a client.
 
No mate: I know it's not infallible but compared to most of them it's pretty good, my first one got stood on by some lump of a Builder & the only 1 I could get quickly was a Di log. Damned thing would show the air was live, took it back & they gave me some other make & that picked up ghost voltages all over the shop. so went & bought another MK & am sticking with them.

I am the opinion that ALL non contact "meters" are a waste of space............
 
It's British gas, they use non contact kew sticks, then recorded the voltage using a metrell I think. The kew stick lit up, which is fail one for them and they won't go anywhere near it now!
none of my testing equipment can register a proper voltage (kewtech kt64 and fluke avi multi) but the kew stick is definitely lighting up!

The gas fitters simply stick the pen tester on the pipe, therefore it is the potential difference between the gas pipe and where they are stood. Or is that a little simplistic?

Yep, I've had exactly this with a client. Absolutley nothing wrong anywhere. In the tank area where the gas 'engineer' was waving his stick, there were wires for the immersion and also ch controls.

What voltage did you measure between the pipes and met?
what was your continuity from the pipes to met?
was bonding continuity satisfactory?
was Ze satisfactory?

There's four pages here and unless I'm blind I cannot see a single test result anywhere.

I'll put up a tenner there's nothing wrong.
 
I am the opinion that ALL non contact "meters" are a waste of space............
look..it aint a "meter" ....isn`t a volt stick...and should never be treated as such....but they aint a "waste of space"....as long as you know the limitations of em...and always remember that they aint intrinsically safe and should never replace an approved voltage indicator to GS38....for the purposes of doing a safe isolation etc.....
 
look..it aint a "meter" ....isn`t a volt stick...and should never be treated as such....but they aint a "waste of space"....as long as you know the limitations of em...and always remember that they aint intrinsically safe and should never replace an approved voltage indicator to GS38....for the purposes of doing a safe isolation etc.....

Meter in quotes you will notice..... As for intrinsically safe ??? what explosive atmosphere would you encounter in a domestic situation?
 

Reply to Voltage on gas pipe to boiler - newly qualified question!! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
857
Hello What was the conclusion of your problem?
Replies
1
Views
809

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top