Just investigating a tingle - on our own utility sink! Its a TNC-S system, all circuits check out, bonding to utilities new and good and checks out OK, check earth contuinity on all appliances. Tingle still there when all circuits de-energised for over half and hour. ZE = 0.20 but has a voltage of 10v through me at the sink, that's without shoes on a slate floor. Can anyone help?
TIA
Regards, David
Just investigating a tingle - on our own utility sink! Its a TNC-S system, all circuits check out, bonding to utilities new and good and checks out OK, check earth contuinity on all appliances. Tingle still there when all circuits de-energised for over half and hour. ZE = 0.20 but has a voltage of 10v through me at the sink, that's without shoes on a slate floor. Can anyone help?