I have put a rod in, no voltage between sink and rod.
Napit inspector came today said their would only be a potential voltage between the two earths if their was a voltage on our earth or the PME.
The DNO guys did agree we havd a PME voltage when they measured from the cut out to my earth.
Regards, David
Update :: Apologies for the delay. (Rather ironic as it's a pet hate of mine when people post and dont have the decency to update)This situation is now resolved. Thanks for all your advise - there are so many helpful members here. I had been using a rod but now back on P.M.E. and vac of 0.2. A month or so ago the whole street lost power for a 7 hours. DNO came out and dug the road up overnight and fixed something! It could be a coincidence but the potential vanished when the job was done. It's a shame I did not have the presence of mind to ask them what they did. What do you think?Kind Regards, DavidAbsolutely not, I've seen this on a property with sandstone floors on a PME supply, a voltage of 5-15 volts between the PME terminal and 'true earth' at the floors. We abandoned the PME and created a TT system which solved the problem completely.