V

VMan

Hi Guys,
Just reading through my spam and got an email for a voltage optimiser - claiming to save you money by reducing the voltage!!!

MyPlanet Voltis Voltage Optimiser

To me this is bull, if something need 1kW to work then it will consume 1kW..no?

My Math example:

At 240 volts:

1000watt appliance = 240 volts x 4.16Amps (240 / 4.16 = 57.7ohms)

My said appliance is heating a said volume of water and needs 1kw to boil. i.e 1000Watts for one hour

------------------------------

if i put a voltage reducer to 218V

At 218 Volts:
( V/R = I ) 218 / 57 = 3.77Amps

(P = I x V) 3.77 x 218 = 821.86 watts - ok customer maybe convinced and may buy one.


Now my said appliance still needs to boil the same amount of water, and will need the same amount of energy.

So 1 hour of the appliance on will only heat the water to 82% of needed value. there for will need to be on a total of 73mins to heat said water (deliver 1kW of energy to the water) - well maybe a bit more due to heat losses whilst heating the water.?!?!

so 1 Kwh will still be 1kWh regardless of voltage?!?!?

Am I right or wrong? or can anyone else explain how this may work -

(I believe a kW meter does not record Power factor(where a k/VA meter will) so even the power factor bull isn't right here.)

cheers
 
I did look at the Vphase units seriously, they were being promoted at a NAPIT conference and that is how i heard of them. What was clear is that they are not design to do anything other than drop the output volts and realistically the VA they can handle is limited even for a domestic. As already mentioned anything that is a heating load is automatically ruled out so this limits the installation to the lighting ccts and sockets in some parts of the house as there is some energy savings due to reduced losses in PSUs that are scattered around the house. I was interested in it for a client that was enduring a supply voltage of 250+ and his bulbs were blowing weekly / daily. In the end i converted them to a combination of low voltage and fluorescent.
Personally i cannot see them adding much value
 
They are based on multi tapped auto-transformers with solid state switching. Any transformer will have inherent losses. As the load increases the higher the losses. It then reaches the point where it goes in to bypass. Even at minimal load you can’t escape the transformer losses.

Many years ago I did an experiment on a large scale. Four 20MVA 33/11KV transformers with on load tap changers. Over several weeks I lowered the voltage available the plants. Voltage went down, current went up.
1KW = 1KW no matter what you do to it.
 

Reply to voltage Optimiser - A Load Of Bull?!?! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
705

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top