Done an install a couple of years back in a large building with three large sub switchrooms fed from a common main switchroom.
All lighting throughout the installation is either hf fluorescent or pl. As I say this was installed around 2 years ago with only the odd lamp failure as would be expected.
Recently lamps have been failing more or less daily and the client got us to relamp all fittings around 4 weeks ago which has been done.
On a daily basis there are numerous lamps failing so I called in today to investigate.
First thing I noticed was most of the lamps that are still lit have blackened ends so I tested the voltage at random fittings and the highest voltage I measured was 218V. Checked a couple of the local DB's and again voltage was around 218 - 219V L-N.
Got into the sub switchrooms and noticed that voltage optimisers have been installed that have been set to 380V L-L.
I'm reckoning that these voltage optimisers are causing the lamp failures. Any opinions welcomed.
All lighting throughout the installation is either hf fluorescent or pl. As I say this was installed around 2 years ago with only the odd lamp failure as would be expected.
Recently lamps have been failing more or less daily and the client got us to relamp all fittings around 4 weeks ago which has been done.
On a daily basis there are numerous lamps failing so I called in today to investigate.
First thing I noticed was most of the lamps that are still lit have blackened ends so I tested the voltage at random fittings and the highest voltage I measured was 218V. Checked a couple of the local DB's and again voltage was around 218 - 219V L-N.
Got into the sub switchrooms and noticed that voltage optimisers have been installed that have been set to 380V L-L.
I'm reckoning that these voltage optimisers are causing the lamp failures. Any opinions welcomed.