Done an install a couple of years back in a large building with three large sub switchrooms fed from a common main switchroom.
All lighting throughout the installation is either hf fluorescent or pl. As I say this was installed around 2 years ago with only the odd lamp failure as would be expected.
Recently lamps have been failing more or less daily and the client got us to relamp all fittings around 4 weeks ago which has been done.
On a daily basis there are numerous lamps failing so I called in today to investigate.
First thing I noticed was most of the lamps that are still lit have blackened ends so I tested the voltage at random fittings and the highest voltage I measured was 218V. Checked a couple of the local DB's and again voltage was around 218 - 219V L-N.
Got into the sub switchrooms and noticed that voltage optimisers have been installed that have been set to 380V L-L.
I'm reckoning that these voltage optimisers are causing the lamp failures. Any opinions welcomed.
 
[ElectriciansForums.net] Voltage optimisers and lighting


http://www.powerperfector.com/powerPerfectorPlusunitsizes
 
Last edited by a moderator:
Thanks Tony that's super. All information has been passed to the consultant that designed our original works. Hopefully there will be a resolution in the next few days :)
 
Last edited:
Good technique, test for obvious and make out a short report so you can warrant slapping them with an invoice. Then fire it back at the designers/consultants and leave it with them to fight it out between themselves.
 
Good technique, test for obvious and make out a short report so you can warrant slapping them with an invoice. Then fire it back at the designers/consultants and leave it with them to fight it out between themselves.

Tbh we got paid to do the complete re-lamping by the client as around half the fittings were out at the time. Now we have had a few extra visits to re-lamp individual fittings but that's part of the game. Don't think it will be long until they get it sorted as there are around 10 fittings that are out since the weekend.
 
Just a random thought, might be worth measuring the voltages P-N at the local DB feeding the lighting, i.e. L1-N, L2-N and L3 - N , to see if there is any major difference. One bodge solution maybe to change the phase the lights are on to get closer to manufacturers 240 +-6%
 
.......Don't think it will be long until they get it sorted as there are around 10 fittings that are out since the weekend.
That's a massive failure rate or FAMTBF (Fu*k All Mean Time Between Failures) as it's sometimes known. I'm still sceptical it's due to such a marginal undervoltage. Most brand name manufacturers build in sufficient tolerances to allow at least 5% below the stated voltage requirement on the product.
 
Just a random thought, might be worth measuring the voltages P-N at the local DB feeding the lighting, i.e. L1-N, L2-N and L3 - N , to see if there is any major difference. One bodge solution maybe to change the phase the lights are on to get closer to manufacturers 240 +-6%

All phases to neutral are the same at the db's give or take 1/10th of a volt.
 
That's a massive failure rate or FAMTBF (Fu*k All Mean Time Between Failures) as it's sometimes known. I'm still sceptical it's due to such a marginal undervoltage. Most brand name manufacturers build in sufficient tolerances to allow at least 5% below the stated voltage requirement on the product.

I agree but I can't think of any other logical reason for the failures as all fittings have been fine since installation. Around 120 - 130 fittings out in 3 months since these optimisers where fitted.
 

Reply to Voltage optimisers and lighting in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
314
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
836
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
948

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top