T

toast

230V single phase supply.
6amp Lighting circuit, T&E 1.0/1.0
Readings
Highest r1+r2=1.72
IR: L-N, L-E, N-E all >299 Mohms
But when energised there is voltage reading across the conductors at the board as follows:
N-E 112V
L-N 107V
L-E 107V
Then at the light fittings:
N-E 127V
L-N 240V (closed circuit)
L-E 7V

The voltage readigns were taken with Line and neutral terminated at MCB and neutral bar respectively but with CPC/Earth not connected at Earth bar.
The circuit does not trip when energised.
Any thoughts of why this is occurring?
 
Firstly why did you test the voltage with the CPC disconnected?
Secondly, think about what you havent done, and why you are experiencing the problems that you are.
Thirdly think about what you have done again, and why this might stop the circuit from tripping if there is an earth fault!

You should be able to answer your own questions if you think about it.

Cheers..........Howard
 
There had been a unit swap (not by me) and the installer called me as they had got a belt of the CPC. that is why I tested as I did.
I can only think that it is a polarity problem as I get continuity with earth and IR readings are really good.
But I tested all Perm lives at fittings, so if it polarity must be connected incorrectly within voids or walls.

All other circuits test off fine.

I know without earth connected there will be no earth fault.
 
Last edited by a moderator:
where did he get a belt off the cpc? consumer unit end or at the light? if hes changed the CU and the lighting circuit worked fine previously then its something hes done, maybe nicked a cable when screwing the CU up?
 
Con unit
I was informed reason for unit change was that there had been fusing issues. But the information I have received regarding this, so far is vague.
But if cable nicked, I would expect IR issues!
 
he sounds like he doesnt have a clue. id be checking everything again, if hes stupid enough to do that god knows what else hes done.
 
May sound scary but I wasn't there at the time. So don't know the reason behind this, just know that he got a belt, which then led me to testing as I did.
 
he sounds like he doesnt have a clue. id be checking everything again, if hes stupid enough to do that god knows what else hes done.

Well that is a fair assumption, I did disconnect all the circuits and reinstalled, without the aid of any pre-planned EIRC and a young family with pregnant mother complaining about the heating and Jeremy Kyle being off.
All other circuits tested off fine.
This is genuinely not a wind up.
 

Reply to Voltage reading puzzle in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
767
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

Induced voltage can be a bit of a red herring when using DVM my guess is somethings moist.
Replies
5
Views
421
T
  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
759

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top