It's mixed bag some fittings are looped-in at ceiling and others are junction/jointed in void.is it loop in?
id be trying to break the circuit down and find what leg your fault is on.It's mixed bag some fittings are looped-in at ceiling and others are junction/jointed in void.
id be trying to break the circuit down and find what leg your fault is on.
That is my next move, just a little puzzled why this fault could occur. Never come across it before.id be trying to break the circuit down and find what leg your fault is on.
i always enjoy stuff like this, gives you a greater sense of satisfaction when i find the fault, unfortunately with our line of work these things occasionally crop up.That is my next move, just a little puzzled why this fault could occur. Never come across it before.
The circuit is on two levels, my thought were to disconnect the supply that enters the loft. Then test the level below, hopefully eliminating one floor.I'd be doing dead tests at different fittings!
Hes said hes already IR tested and its clear, but im inclined to think id be doing them again!I'd be doing dead tests at different fittings!
Indeed, and once you have diagnosed the fault, it's in your armour.i always enjoy stuff like this, gives you a greater sense of satisfaction when i find the fault, unfortunately with our line of work these things occasionally crop up.
Only you'll know whats easiest, did the guy only change the CU? wasnt poking around in anything else?The circuit is on two levels, my thought were to disconnect the supply that enters the loft. Then test the level below, hopefully eliminating one floor.
Hoping that the fault lies within the loft as access is easier.
Hes said hes already IR tested and its clear, but im inclined to think id be doing them again!
Yes the IRs came up brand new, I did test twice but there were people in the house, may be that a switch could have been opened then closed without my knowledge.Hes said hes already IR tested and its clear, but im inclined to think id be doing them again!
.An IR test on a circuit with a "break" on it or loose connection isn't going to tell you anything, whereas a R1 + R2, R1 + RN, R2 + RN to confirm the continuity of all conductors followed by IR would be of more use.
I did ask the question and claims not to have touched anything else, other than the CU. Which also seems to be confirmed by what the occupants are telling me.Only you'll know whats easiest, did the guy only change the CU? wasnt poking around in anything else?