been to look at a job with a long main supply approx 60m long underground 25mm 3core SWA running off a 100amp fused isolator.
meter position is at drive entrance and house is approx 60meters away.
not done a voltdrop calc for ages so can someone correct me if i,m wrong.
this is a new build from 3 years ago which has changed hands and new owners have built a huge double garage that needs wiring.
first look i thought it was to small for the length of run but my calc seems to put it ok.
1.64 x 60 x100
------------------- giving 9.84 v with 11.5v being max as i recall
1000
meter position is at drive entrance and house is approx 60meters away.
not done a voltdrop calc for ages so can someone correct me if i,m wrong.
this is a new build from 3 years ago which has changed hands and new owners have built a huge double garage that needs wiring.
first look i thought it was to small for the length of run but my calc seems to put it ok.
1.64 x 60 x100
------------------- giving 9.84 v with 11.5v being max as i recall
1000