Some Wago connectors are rated at 24 amps and take cable up to 2.5mm. Would you use them on a ring main circuit?
My concern is that if one leg of the ring went open circuit, the wago would be then used on a radial circuit protected by a 32a mcb.

Bul
 
Considering that 2.5mm cable is also rated at 24A (before any correction factors), yes.

Your concern is justified, and that is the reason why I never use ring final circuits, I always wire in radials on 20A breakers.
 
2.5mm cable is rated at 27amps before any correction factors. Nothing wrong with ring finals or 24 amp wagos on a ring, ok if it goes "open circuit" then the circuit has been damaged, the same way a radial circuit might be damaged and loose its cpc.
 
The point is that if the ring circuit becomes a radial circuit the 24 amp rated wago would be on a 32 amp circuit.

The 2.5mm cable is also rated at 24A. If the ring became a radial, the 24A cable will also only be protected by a 32A breaker. There is no issue with you using the wagos.

Edit: Jonny66 beat me to it :D
 
2.5 is rated at 30A.

On tray in free air!!

Great news! Lets all wire our rings on tray and in free air from now on! I quite like the 'industrial look', I reckon it will go well in the living room! I don't think it will take much persuasion to get my customers thinking the same way :D
 
Great news! Lets all wire our rings on tray and in free air from now on! I quite like the 'industrial look', I reckon it will go well in the living room! I don't think it will take much persuasion to get my customers thinking the same way :D
I know some steam punk type people who would love that look in their houses, cheaper than MICC... :lol:
 

Reply to Wago connectors in a ring main in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

The repair kit is actually sold by WAGO for that specific purpose (in the wall repair). I had wondered myself about shrinking individually first...
Replies
4
Views
530
Yep! Edit button was disabled by the time I seen it. Hopefully the 15m/15m clarified what I intended 😀
2 3
Replies
36
Views
2K

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top