This is going to sound stupid but when testing the continuity of bonding conductors does everyone else connect a lead to the met then test the from the lead to the cable?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss wander lead in the UK Electrical Forum area at ElectriciansForums.net
the 0.05 ohms is the reading you should get between separately bonded services, e.g. water to gas. the resistance of any bonding cable will depend on it's length and csa. e.g 10mm is 0.018ohms per 10m.