D

Dave 85

Hi lads
Just looked at wiring a warehouse about 20m by 20m and thought I'd get some opinions on a few things.
I've done a bit of industrial but am 95% domestic. (Not domesticated though)

Its an empty industrial unit at the mo with just a new 3phase board and nothing else. Its gonna be used as a workshop for building luxury log cabins.
So heres what im thinking:
PVC conduit run horizontaly a meter off the ground to feed all the sockets. Is this adequate you reckon? I don't do steel so its that or SWA
6 Metal Halide 250w lights, wired in SWA-Are these the best type of light? is 6 enough?
RCBO's on the sockets-Im tempted not to bother, what do u guys think?

Any thoughts would be much appreciated
 
Sorry if it's stating the obvious, but you really need to speak to the customer to identify what types of equipment they plan to use, that will start to allow you to design what's required (does your PL insurance cover design?). Knowing what machinery is going to be used will also help on the lighting design.

Are you also being asked to provide EM lighting and fire alarm, again PL insurance cover?

Hope that's a starter for 10!
Regards.
 
most wholesalers will do you a lighting design if you give them athe relivant measurements and what its used for!
met halide better than sons but the new type energyefficent low- bay modulars are alot better but pricey.

also check how many 3 ph circuits the want may be better to run 2x2 galv trunking if theres alot of circuits.

better to get a floor plan off the company telling you what they actually need.
 
Dave, i do these size units all the time - with 20 x 20 i do three rows of three lights. I know you say you dont do metal, but, for the lights.. go up and over the building with trunking, pipe along to the lights from the trunking with pvc pipe using thro boxes etc, and plug in ceilling roses to the lights. This makes it much easier than SWA to wire to the switches etc. For the sockets, depending on how many you need, the plastic pipe or swa will be ok, but like others have said - find out what the client is going to instal later - may be better to run trunking around for the future sockets.
 
Thanks for the help lads, from the sounds of it theres only gonna be one bit of hard wired 3 phase machinery but not had a proper discusion really. The prob with metal truning is that the vertical steels protude from the walls about a foot right up to the ceiling, every 6 metres all the way round. So getting past them would be a nightmare. Think this ones gonna have a tight budget so I'm not too concerned about future proofing.
 
First of all check with the customer what kind of plant will be needed around the unit?

will they require compressed air, 110v, 240v, 415v supplies?

What height is the unit?

Id go for RCBOs. you dont want a fault on one circuit shutting down others.

Why?

surface containment, (preferably steel trunking) and use MCB's
 
Definatly would run Galv trunking around for the sockets, easy to add more in future, also use metal clad sockets, and there would be no need for RCBO's, also i would go with what polo said as you will be wanting to spread things out across the 3 phases
 
Doing a warehouse at the moment, off the top 6 lights does not sound enough, you are likely to get bright and dark spots and shadows from HQIs. Think the optimum height for low bays are around 6M but i would check with the wholesaler and get the specs out for the lights, i.e. optimum height and spread, if the walls are painted white that will help. I am doing mine in fluorescent at 3.5M , client prefers it, they are a machine shop. As for wiring, i tend to mix between nice shiny galvo trunking and SWA with some SY for machines, it all depends on the final look, as you said you have some obstacles. Sometimes i go right up and across the roof if it will look naff, routing around colomns and the like. As for sockets i would run minimum of two radials on RCBOs C20 breakers. Easy with SWA or drop down from trunking as mentioned. Would also check to see if they are using any 110V stuff as they may need a trany and some yellow sockets for those.
Basically you start with all the load devices, get everything out of them possible about what they intend to use and then work backwards to the board and hopefully the supply is big enough :)
Oh and don't forget HQIs will need C breakers.
Oh and what about heating, i am using some radiant jobbies from dimplex
 
Last edited:
Doing a warehouse at the moment, off the top 6 lights does not sound enough, you are likely to get bright and dark spots and shadows from HQIs. Think the optimum height for low bays are around 6M but i would check with the wholesaler and get the specs out for the lights, i.e. optimum height and spread, if the walls are painted white that will help. I am doing mine in fluorescent at 3.5M , client prefers it, they are a machine shop. As for wiring, i tend to mix between nice shiny galvo trunking and SWA with some SY for machines, it all depends on the final look, as you said you have some obstacles. Sometimes i go right up and across the roof if it will look naff, routing around colomns and the like. As for sockets i would run minimum of two radials on RCBOs C20 breakers. Easy with SWA or drop down from trunking as mentioned. Would also check to see if they are using any 110V stuff as they may need a trany and some yellow sockets for those.
Basically you start with all the load devices, get everything out of them possible about what they intend to use and then work backwards to the board and hopefully the supply is big enough :)

We swear by HF Anti corrosive 6ft twins run with Trifos daylights , I am sure you will already know but for those that do not make sure you run your fluorescents across at least two phases or just use HF fittings to stop the stroboscopic effect .
 
Fabrication workshop, dealing (and moving around) with heavy log's!! PVC conduit just isn't up to the job as far as mechanical protection is concerned. It NEEDS galvanised conduit, preferably dropped from suitably sized metal trunking that runs around the walls at a suitably high enough level out of harms way....

Don't have much of a problem with using PVC conduit on the roof lighting layout, but switch drops should also be made in galvanised conduit. As already mentioned all switches and general purpose socket outlets etc, should be of the metal clad type. 3ph outlets can if intelligently positioned, be of the high impact plastic variety....

This really should be looked at, as an industrial installation rather than a commercial one. They will be using some pretty large machinery that can cope with long lengths of raw logs etc....
 

Reply to Warehouse Job in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
284
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top