Washing machine trips the circuit. | on ElectriciansForums
Discuss Washing machine trips the circuit. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Goody
London
Customer rang to say his washing machine trips the circuit in the middle of the cycle. He said, it ran for a while and stopped. Enquired on the phone and it looked like it only tripped the MCB and the RCD stayed on.
It's on a radial circuit with 16A MCB. Could someone shed some light on this. Many thanks! :banghead:
If the rcd goes i would also say heater which should go in the first 2 mins as it goes under water in filling but only the mcb going in middle of cycle so most likely the pump as it has no earth. just my take.
Thanks guys, the new board (CU) went in on Saturday and the chap rang me today. You know what he will say when I see him, "it was quite alright before the board change, now you are blaming it on my washing machine...":73:
Don't know What to say !!!!! :innocent:
You test the installation not his appliances.
On a mains change i always say to give it a week as most household appliances have been used by then to see if any have a fault.
It just makes your job easier when the call comes........
Thanks, but then how am I going to convince him that his equipment was faulty and nothing to do with the new board.
Because when you remove the offending part from his washing machine hopefully physical evidence of deteriation will show
Sent from my GT-I9100 using Tapatalk
Hard to convince a customer their stuff is faulty when it was working before a CU change, as they asume the new CU is better (as it is) but they can't see it that way. I doubt if in 2 mins the washer would've filled up/done a prewash and started to pump out, heater elements are the usual suspects or a combination of an old worn motor drawing too much and heater combined just tripping the mcb.
If the MCB is going and not the RCD then it is a fault line to neutral, the fact that it is going half way through the cycle seems to indicate that the w/m is taking overcurrent for an hour and then tripping. If the radial is a dedicated circuit for w/m then try a power meter or clamp the cable to see what is being drawn. If it is a shared circuit then see if there is another heater on the circuit taking about 1800W, then up the MCB to 20A (cable permitting).
We really require more information:
1) Make and model of washing machine.
2) When the MCB tripped was the drum full of washing in dirty water, clean water, little water, or no water?
3) Will the MCB reset and if so will the machine run and how long?
4) If the machine will run and drum is full of washing in water, can the programmer be set to pump and the drum emptied of water?
Had one years ago brand spanking new washing machine tripping RCD half way through cycle turned out to be one piddly cable hadnt been cliped correctly and the 5 times usage had let it rub against side of machine causing trip but only on that part of cycle Woman would not beleive that her BRAND NEW!!!!!! washing machine was at fault
Fitting a new C.U. can bring to light problems like this as rewireable fuses ect old mcbs may have been able to take the overcurrent for periods of time greater than new kit fitted Goodluck convincing her tho
Id give local Appliance repair guy a wee ring n ask how much he would charge to check machine over and if its not to much suggest to client this would be the way forward as your NOT an appliance engineer and some appliances have more electronics ect that you may damage by testing wrongly
Reply to Washing machine trips the circuit. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
You may still have a problem with earth leakage though, it could be that the Samsung has less leakage than the Bosch ones. If you do get a random...