On a domestic job today and came across an unusual bonding setup. The main house is TNC-S, supply to remote home office via SWA cable. The remote building has an oil fired boiler and the copper pipe work has a 10mm bond cable going out through the external wall to an earth electrode. The electrode is only connected to the bonding, nothing else. Does this or does this not make the bonding cable an extraneous conductive part and therefore require bonding?
 
Yes it an exported TNC-S via the SWA armour. I would have difficulty in changing it to TT now since a new solar PV installation is using this cable to feed back to the main house and incoming supply. (see my other thread "Naughty naughty")
 
Last edited:
So if they've exported it why havent they run the bonding to the local earth bar?!?
I cant even think of the readon what made them think they could do it.

Sent from my GT-I9100 using Tapatalk
 
I reckon someone didn't know what they should do, got told they have to use an earth rod, or if they export the PME they have to use 10mm² bonding conductor, so did both.
 
The armour won't have the equivelant conductivity of a 10mm² copper conductor, and it's the earth/bonding conductor that's the extraneous-conductive-part.
If it was removed, there wouldn't be anything that required bonding.
Depends on the SWA size but if it is the earth for the building it should be OK for bonding, presumably the oil fired boiler and/or copper pipework would need bonding as an incoming service?
 
No, you'd have to have a 70mm² 3core SWA cable, before the armour had the same conductivity equivelance as 10mm² copper.
Just noticed, that it's an oil fired boiler, for some reason I thought it was a wood burner.
Appologies.
The oil pipe is most likely an extraneous-conductive-part, so will need bonding, unless it's plastic, same thing for water.
You'll need a 10mm² core in the SWA to use as a bonding conductor, or the office will have to be made TT.
You could technically use a conductor from the office CU to the rod, picking up any pipework on the way.
That would allow you to leave the existing cable in situ, and just crimp a new length of cable on to it.
 

Reply to Water bond to earth electrode. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top