View the thread, titled "Watts to Amps" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

sirkits origional post is correct it acounts for inrush current such as a motor starting ect or high frequency stuff. They will take the much larger inrush current for a longer period but not indeffinatly.

But a B6 breaker will still trip at 30 amps in 0.1 of a second, which is quite smaller than the 30 minutes that he suggested it would hold for. And the same goes for a C6 tripping instantaneously at 60 amps and a D6 tripping instantaneously at 120 amps. I'm sure when we all started we wondered why a loop test was tripping our type 1 5 amp MCB didn't we? Even B6's go sometimes too....
 
Last edited:

Reply to the thread, titled "Watts to Amps" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top