Why is it clicking on off on off on off?
[automerge]1570227265[/automerge]
I understamd what you mean about the 10 ohms between live and earth but thats what im getting and there is def not 20A therei can touch the casing.
 
Before you next visit, buy yourself one of these voltage testers:

B&Q Pen-type Voltage tester | DIY at B&Q - https://www.diy.com/departments/b-q-pen-type-voltage-tester/177924_BQ.prd?ds_rl=1272379&gclid=CjwKCAjw_uDsBRAMEiwAaFiHa9ZxwsRXbRxw2NxxTNm5nvcGXgOFmmLoteDnUAVaLyMfwdiwjUu4JRoCGBMQAvD_BwE&gclsrc=aw.ds

Check it works first by touching something definitely connected to terra firma eg: a metal post in the ground. Then test it touching something electrically earthed eg: your home MET. Then test it on the Line side of a switch and then on the switched Line in the on and off position. Also touch the securing screw and neutral. Now you have a feel for the sort of voltage readings you will see. You use the 'direct contact' metal pad to put your finger on.

At the client's home with all turned on except for the light switches, walk up to a switch. Put your finger on the direct contact pad and then touch the securing screw with the tip of the voltage tester. What voltage reading do you observe? If it is a steady voltage then it is a potential due to leakage current flow or typical combined NE to local terra firma potential difference. If there is a brief rise in voltage and then fall to zero the likely cause is you being discharged to the screw; if this is what you see happen remove the tip for the screw, count to ten and then retouch the screw - what do you observe? I would expect you to see a steady 0V or very low voltage which indicates no potential difference between you and the screw.

Now, walk away from the switch and around the room/home for a minute and return to the switch. Touch the screw to discharge yourself. Then use the voltage tester and observe the reading. I would expect it to steady 0V or very low.

Now repeat all the above with the light switch on.

Hope this helps. Let us know what you find please.

:)
 
Last edited:
The Megger 1700 series does have a touch voltage contact. Thats why I asked which Megger it was. Just waiting for a Mod to approve my posts. In the meantime;
 
99.99% this is indeed just static.

A shock caused by an electrical fault will be continuous - all the time you remain in contact and every time you touch the 'live' point, you will receive the shock. Static requires you to charge up your stray capacitance (to earth) by friction or some other means, during which the charging current is too small to notice although the ultimate voltage can be very high. Then, when you touch something earthed (or conductive and large in size which has a large stray capacitance to earth itself) your own stray capacitance discharges suddenly with a current that is large enough to feel. Then you feel nothing until you have charged yourself up again.

A good demonstration would be to get into a position where you would receive a shock from the switch but stand on an insulator such as a piece of dry wood or plastic before doing so. Your resistance to earth will then be guaranteed to be much too high to allow enough current to flow from a 230V electrical fault to be felt as a sudden shock. If you get the shock, then nothing, you have proven it was caused by your stray capacitance discharging.*

Your Zdb reading is good enough that there is no reason to suspect a disconnected CNE upstream, and there are none of the usual symptoms of the lights flickering and blowing and going very dim when anything else is turned on. It would not however manifest as a voltage between N & E within the system as they would still be connected together at the service terminals; rather between earth as defined by the equipotential zone in the house, and true earth outside. Your Zs at the switch also looks normal and indicative of a good enough earth that if there is a serious leakage or intermittent short from line, the OCPD will trip.

*Note incidentally that the stray capacitance of the body is high enough that you can sometimes detect a steady, faint tingle / buzz corresponding to a fraction of a milliamp of AC leakage if you brush lightly against a truly live metal surface, but that is not the effect described here.
 

Reply to the thread, titled "Weird Earth Fault" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Weird Earth Fault
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
37

Advert

Thread statistics

Created
ThrownRazor25,
Last reply from
Lucien Nunes,
Replies
37
Views
4,389

Advert

Back
Top