Discuss Wet UFH pumps causing RCD tripping in the Central Heating Systems area at ElectriciansForums.net
Turning on the UFH, the wiring centres go through a start up process then send power to the Neostats. They in turn go through a start up process and then turn on sending a signal back to the wiring centre to turn the boiler on. It's at this point that the RCD trips.
One post seems to contradict the other here, you can't start the system but then it trips overnightThe RCD generally trips over night so other appliances are on but not being used.
Forgot to mention this is a new build and all appliances are new.
I will try to move to an RCBO to test.
If a brand new RCD is tripping at that level I would be speaking to the manufacturer about a replacement, out of the box problems with RCD's seem to be getting more common in the last few yearsRCD ramp test indicates that it's tripping around 19mA.
1/2 test indicates no problems.
The initial tripping was intermittent and would happen overnight. The system would operate happily for 3-4 days then trip out.One post seems to contradict the other here, you can't start the system but then it trips overnight
If a brand new RCD is tripping at that level I would be speaking to the manufacturer about a replacement, out of the box problems with RCD's seem to be getting more common in the last few years
No leakage clamp meter as yet, any recommendations?
Good ones aren't cheap, sadly. I had a Metrel one (can't remember the model) that was amazing as it would even give you an indication of the nature of the current, lead/lag, pf etc etc which was genuinely helpful in understanding what was going on in the circuit, cost about ÂŁ400ish ten years and some pikey stole it in a van break-in. Now you can get good ones for half that.No leakage clamp meter as yet, any recommendations?
There is no N link between the boiler and the UFH as the wiring centres use a 0v built in relay to send the demand signal.
The remote Grundfos pumps and 2 port valves are controlled by the boiler spur, so I could separate the UFH and the boiler to 2 RCBOs
Thanks for that, I've been reading reviews and ordered the Megger DCM305E ÂŁ220.Good ones aren't cheap, sadly. I had a Metrel one (can't remember the model) that was amazing as it would even give you an indication of the nature of the current, lead/lag, pf etc etc which was genuinely helpful in understanding what was going on in the circuit, cost about ÂŁ400ish ten years and some pikey stole it in a van break-in. Now you can get good ones for half that.