Eastbourne, East Sussex
Done an eicr on a 2 bed flat, all good apart from the sockets, it's a radial, wired in 2.5 t+e (25 sockets in total), on a 20 mcb, zs was 2.72 ohms, I've checked against bgb and its over the maximum permitted zs, customer now wants it sorted, but I'm wondering what you guys would think is the best way to go about sorting this out. Choices I can see are, splitting the radial into two, or splitting into two and making the longest leg a radial.
The whole flat has just finished being decorated and all carpets down etc
Rcd protection 1667 ohms.
I see what your saying but I don't see the rcd value of 1667 so that's all ok madam, would rather not rely on that figure, if that's the case then there would have to be a serious problem before it gets over 1667 ohms
Would rather make sure everythingis within the range of the mcb then have the rcd as additional
Zs of 2.72 on a TN system sounds a bit high just to be caused by the length of the circuit, especially if it's just a 2 bed flat...
(you'd be looking at 140+ metres of cable assuming the terminal connections are all good!)
Wouldn't mind betting you could bring it down a fair bit by just going round and tightening all the terminal screws...