Done an eicr on a 2 bed flat, all good apart from the sockets, it's a radial, wired in 2.5 t+e (25 sockets in total), on a 20 mcb, zs was 2.72 ohms, I've checked against bgb and its over the maximum permitted zs, customer now wants it sorted, but I'm wondering what you guys would think is the best way to go about sorting this out. Choices I can see are, splitting the radial into two, or splitting into two and making the longest leg a radial.
The whole flat has just finished being decorated and all carpets down etc