Strictly speaking method C is 19.5 amps. But we won't haggle over 0.5 of an amp. In fact running a 1.5mm directly to the 2 fans is also perfectly safe on a 20amp rcbo. But is it conventional, good practice or advisable? No

Is it not 17.5 amps for a 3 core or am I losing plot again?!

Table 4D2A:

[ElectriciansForums.net] What cable size and breaker would I need for two extractor fans in a public toilet? 1.5mm 3 core and a 20amp rcbo?
 
Last edited:
I was wondering if there were FCU's by the fans and that overload protection was provided that way.
If the rcbo feeds the fans directly than they can be treated like any "End of line" appliance and overload protection omitted. Short circuit protection only required and the 20 amp RCBO covers that
It's likely the RCBO is oversized but can't be sure without knowing more about the fans who knows.
It would be oversized if the 1.5mm was connected to a circuit where the loading can't be controlled directly, like a socket circuit socket
If the OP has a clamp meter it would be interesting to know the current draw with both fans on.
In principle that's not an issue. Both fans won't take more than an amp or 2.Well under the capacity of the cable and the rcbo. The issue is, is the cable going to be protected properly under overload and short circuit conditions. It is Interesting how unconventional situations (like the OP, s) force us to look at a situation that we all know is instinctively wrong but can't immediately explain why (talking about myself here). Then we end up "going back to the drawing board" and having to figure out again.. "Why is this wrong?". Good exercise though!!
 
Is it not 17.5 amps for a 3 core or am I losing plot again?!

Table 4D2A:

View attachment 84376
You are most definately not losing the plot. It's there in black and white (or purple and white). But I think the key is that that 3 core is referring to 3 "loaded" conductors, as in 3 phase, whereas the 3 core referred to by the OP is containing just 2 loaded conductors
 
The issue is, is the cable going to be protected properly under overload and short circuit conditions. It is Interesting how unconventional situations (like the OP, s) force us to look at a situation that we all know is instinctively wrong but can't immediately explain why (talking about myself here). Then we end up "going back to the drawing board" and having to figure out again.. "Why is this wrong?". Good exercise though!!
Thank you for talking that through. I was certainly thinking in terms of overload and fault protection. I get that overload protection could technically be omitted. If (as in the case of many fans) the manufacturer advises 3 amp protection it still doesn't sit right with me that that 60 amps could theoretically flow (B curve) before it shuts off.
Is there a remote possibility of more current being drawn if the if the fan jammed or the windings were damaged and it failed to properly start and just hummed I wonder. Probably unlikely and academic.
 
Is there a remote possibility of more current being drawn if the if the fan jammed or the windings were damaged and it failed to properly start and just hummed I wonder. Probably unlikely and academic.
That's a valid point actually as technically all motors should have overload protection. But the wattage of a standard 4" fan is very low.Should it jam its internal impedence will prevent large currents from flowing and if they did the fan windings would likely burn out long before the supply cable would be troubled. In fact you will sometimes come across fans that have "stuck" and on being released they carry on working. High internal impedence prevents the from burning out
 
Do they make special fans for the UK, different from the millions they make for countries where you can't get any overload protection beyond the circuit OPD?
 

Reply to What cable size and breaker would I need for two extractor fans in a public toilet? 1.5mm 3 core and a 20amp rcbo? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
353
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
320
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
368

Similar threads

  • Question
It’s a single phase 1500w motor. It has a 6 amps speed controller, distance from controller to fan about 3-4 meters .
Replies
7
Views
772
  • Question
I'm familiar with many domestic extractor fans which are primarily class 2 (double insulated) and consequently are not required to be earthed...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top