I have to replace some bathroom downlighters with a single IP44 double insulated light this week (the downlighters were installed by a previous owner as I can see the position of the original central light).
The CU is wylex fuses (ie no RCD protection) and the main bonding is ok.

I am treating this as a like for like replacement and giving the customer a minor works cert (as I do for like for like as well even though not strictly req). Also plan to ensure that the supplementry bonding is up to scratch when I am in the loft.

Just wanting your opinion as it is a special location which seems to have many opinions.

If you think it needs to be a full installation cert then it will need RCD protection as well and the only way I can think of doing this is to install a small (2way) enclosure with a RCBO next to the existign CU and feed the RCBO from the exist light fuse and then feed the bathroom (and upstairs) lights from the RCBO. Comments

Your comments/ opinions.
 
i would try and talk them into a c/u upgraid first but if they dont you could do what you have just explained and supply them with a minor works cert and recommend a board upgraid in your comments but test the circuit first mate for borrowed neutrals as you know this will give you problems with you rcd and dont forget to check the size of your water and gas earthing .
 
Or you could bring the lighting outside the bathroom and feed it back via a 30ma rcd fused spur, then issue an eic.
This saves all that relying on other factors lark. ;)
 
yeah its not really 'like for like' as you have to alter the wiring. What i have done in the past on some rental properties to keep cost down and tick all the boxes is to fit a 30mA RCD into the supply tails of the board...yeah not ideal but its quick and easy. agree with fitting a RCD spur also. is it a wooden wylex board?? if so it has to be changed asap
 

Reply to what cert for this? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

  • Question
The chances of any problem without the RCD are minimal, including it extremely negligible......with the supplementary, on a kin to Hannibal Lector...
Replies
6
Views
749
  • Question
Surely one of the most important parts of supplementary bonding is to bond the radiator and hot tap/pipe to the cold one. Both the hot tap and...
Replies
32
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top