I have just completed an EICR.

All the earths have been chopped off in the ceiling roses and switches on the lighting circuit. There are no class 2 fittings.

Usually if there are no earths on the lights and no class 2 fittings then it will be a C3. However, the lighting circuit does have CPC's they have just not been connected anywhere. Would this be a C2 as Zs will be greater than the maximum? Also, how does this relate to RCD protection? There is RCD protection on everything but with the Zs on the lights being non existent the RCD will not trip with an earth fault (especially in relation to the bathroom).

Cheers guys.
 
I have seen brand spanking new builds where the sparks have simply bent back and cut the cpc extremely short where class II fittings are fitted , just taking the lives and N into the light

I tend to sleeve the cpc and coil it up like a snake leaving it long incase the home owner changes the light
 
Yes but in the original post if I understood correctly by cutting the earths they were then not taking an earth round the circuit to each point, compared to what you are saying where the earth is there but just not connected
 
If the cpc is connected at the ccu but not at each class 2 (as there is no requirement) accessory then would that still be determined as no cpc? The circuit would still have a cpc, no?
The requirement is not that a cpc be present for every circuit. It is that a cpc be run to and terminated at each point in the wiring. This is quite a different thing. So in no way could it be said that you have a cpc at each point in the wiring.

(In fact, it doesn't have to derive from the same circuit - think of containment.)
 
If the cpc is connected at the ccu but not at each class 2 (as there is no requirement) accessory then would that still be determined as no cpc? The circuit would still have a cpc, no?

If the cpc is connected throughout the circuit so that it is present at every point then no it wouldn't be a C2, but I have read the OP as meaning that the cpc has been cut out of both ends of every cable leaving the circuit with no CPC at any points.
 
If the cpc is connected throughout the circuit so that it is present at every point then no it wouldn't be a C2, but I have read the OP as meaning that the cpc has been cut out of both ends of every cable leaving the circuit with no CPC at any points.
Yes, my bad, I hadn't fully read the OP, my apologies.
 
Surely if carrying out an EICR the RCD'(s) shall be tested, and if they pass at that point the argument as to whether they can fail or not is irrelevant as far as the OP's question is concerned!

Reading previous posts it would seem that the continuity of the cpc is unclear therefore I would give a FI (Further Investigation)
 
Yes RCDs can fail, but not because there’s no CPC.
Didn't say that, they can just fail. There's too much reliance on the fact that a circuit is protected by an RCD so therefore a lot of crap situations are tolerated because of the RCD. However, like any other device the RCD can fail and not operate as intended under fault conditions.
 

Reply to What code for all CPC's chopped off on lights? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
385
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
966
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

It’s difficult to advise on an electrical issue when some isn’t very conversant with electrical terminology.
Replies
14
Views
1K
My latest trick for this....if completely desperate and you have 3 very short cables .... Make a hole big enough for a quickwire to fit through...
Replies
8
Views
793

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top