I have just completed an EICR.
All the earths have been chopped off in the ceiling roses and switches on the lighting circuit. There are no class 2 fittings.
Usually if there are no earths on the lights and no class 2 fittings then it will be a C3. However, the lighting circuit does have CPC's they have just not been connected anywhere. Would this be a C2 as Zs will be greater than the maximum? Also, how does this relate to RCD protection? There is RCD protection on everything but with the Zs on the lights being non existent the RCD will not trip with an earth fault (especially in relation to the bathroom).
Cheers guys.
All the earths have been chopped off in the ceiling roses and switches on the lighting circuit. There are no class 2 fittings.
Usually if there are no earths on the lights and no class 2 fittings then it will be a C3. However, the lighting circuit does have CPC's they have just not been connected anywhere. Would this be a C2 as Zs will be greater than the maximum? Also, how does this relate to RCD protection? There is RCD protection on everything but with the Zs on the lights being non existent the RCD will not trip with an earth fault (especially in relation to the bathroom).