I have just completed an EICR.

All the earths have been chopped off in the ceiling roses and switches on the lighting circuit. There are no class 2 fittings.

Usually if there are no earths on the lights and no class 2 fittings then it will be a C3. However, the lighting circuit does have CPC's they have just not been connected anywhere. Would this be a C2 as Zs will be greater than the maximum? Also, how does this relate to RCD protection? There is RCD protection on everything but with the Zs on the lights being non existent the RCD will not trip with an earth fault (especially in relation to the bathroom).

Cheers guys.
 
Wait, so we can apply a code C3 for lighting circuits that have no CPC at all, but it’s C2 if the unused CPCs have been cut off, rather than terminated in a parking terminal?
Questions that should be asked:
It’s not dangerous, there’s no live parts that can be touched, and it’s not potentially dangerous because there are no exposed-conductive-parts that could become live under fault conditions.
Yes improvement is required in order to comply with BS7671 which requires a CPC, in case someone decides to install class 1 fittings or accessories.
 
I have seen brand spanking new builds where the sparks have simply bent back and cut the cpc extremely short where class II fittings are fitted , just taking the lives and N into the light

I tend to sleeve the cpc and coil it up like a snake leaving it long incase the home owner changes the light
 
Yes but in the original post if I understood correctly by cutting the earths they were then not taking an earth round the circuit to each point, compared to what you are saying where the earth is there but just not connected
 
If the cpc is connected at the ccu but not at each class 2 (as there is no requirement) accessory then would that still be determined as no cpc? The circuit would still have a cpc, no?
The requirement is not that a cpc be present for every circuit. It is that a cpc be run to and terminated at each point in the wiring. This is quite a different thing. So in no way could it be said that you have a cpc at each point in the wiring.

(In fact, it doesn't have to derive from the same circuit - think of containment.)
 
If the cpc is connected at the ccu but not at each class 2 (as there is no requirement) accessory then would that still be determined as no cpc? The circuit would still have a cpc, no?

If the cpc is connected throughout the circuit so that it is present at every point then no it wouldn't be a C2, but I have read the OP as meaning that the cpc has been cut out of both ends of every cable leaving the circuit with no CPC at any points.
 
Surely if carrying out an EICR the RCD'(s) shall be tested, and if they pass at that point the argument as to whether they can fail or not is irrelevant as far as the OP's question is concerned!

Reading previous posts it would seem that the continuity of the cpc is unclear therefore I would give a FI (Further Investigation)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
What code for all CPC's chopped off on lights?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
28
Unsolved
--

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
dksanders,
Replies
28
Views
5,838

Advert

Back
Top