Just done a pir and all ok but in garage area all cables twin and earths are clipped direct to brick work for about 5metres would you code this possibly code 3 or let it go should be in trunking for me
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss What code in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I agree, but what reg covers this ?cables below 2 meters or at risk from mechanical damage should be mechanically protected. if you think there's a risk of damage, make it as a note in the comments section.