What are the odds on that SY braiding not being Earthed?
Pretty good I reckon :rolleyes:
Does it require earthing?
It’s not an exposed-conductive part as it’s under the clear sheath.
It’s no use as a CPC.
I doubt it would function as an earthed metallic sheath if the cable were penetrated by a metallic object.
 
526.9.1 Connection of multiwire, finewire and very finewire conductors
In order to avoid inappropriate separation or spreading of individual wires of multiwire, fine wire or very fine wire conductors, suitable terminals shall be used or the conductor ends shall be suitably treated.
It does not state “ferrules’.
A long standing practice for protecting such wires is to twist the exposed strands together and then fold them over.

Whilst we are allowed to design, install and initially verify installations to the 18th edition, inspection and testing of existing installations should be conducted to the current edition.

Hmmm, isn't a ferrule a terminal?

And, in BGB: BS7671:2008:Amd 1:
526.9.1 In order to avoid inappropriate separation or spreading of individual wires of multiwire, fine wire or
very fine wire conductors, suitable terminals shall be used or the conductor ends shall be suitably treated.
 
Hmmm, isn't a ferrule a terminal?

And, in BGB: BS7671:2008:Amd 1:
526.9.1 In order to avoid inappropriate separation or spreading of individual wires of multiwire, fine wire or
very fine wire conductors, suitable terminals shall be used or the conductor ends shall be suitably treated.
No a ferrule is used to treat the end of a conductor.
The terminal is the part with the screw.
In the case of MCBs, the terminals are designed so the screw part of the terminal does not make physical contact with the conductor.
The neutral bar however in the top picture has nothing to protect the conductor from the screw.
 
I hadn't noticed the hinges look nackard in the photo too, and also there's a window for the breakers? how well does that fit? that thing is basically f****'d in so many ways:D :p
The reason the hinges are nackard is because there is a water pipe obstructing the opening of the lid and it has been forcibly opened in the passed.
 
Does it require earthing?
It’s not an exposed-conductive part as it’s under the clear sheath.
It’s no use as a CPC.
I doubt it would function as an earthed metallic sheath if the cable were penetrated by a metallic object.
Good point,Swa as a covered sheath,& not always used as cpc,but is earthed
 
No I haven't but I can tell you it's a Hager. I won't be going back as after pointing a few things out to the owner he has appointed another electrician to do the report.
in other words he wants a tick-box satisfactory report for peanuts. yous best off out of there.
 
20p : Containment - when the lid is down is the IP rating achieved? Can the lid be secured so that a tool is needed to open it? If not, then seeing a bit of exposed copper makes me go for my C2 bat. Am I too harsh?
 

Reply to What do you code these? Commercial installation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Understood, ; ) i'll pass it on to a company who do them day in day out i think.
Replies
8
Views
851
It was purely an off the top of my head example, but I'd say - accessible live parts C1 - inaccessible live parts C2 - 10 feet up in a locked room...
Replies
9
Views
731

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top