What do you think about a 16A socket on a 20A breaker | on ElectriciansForums
Discuss What do you think about a 16A socket on a 20A breaker in the UK Electrical Forum area at ElectriciansForums.net
bill01803
Devon
Been asked to provide a 4 pole 16A socket with RCD protection with a C20 protecting the circuit specified by the manufacture of the machine, should I not use a 32A socket?
can't see a problem as long as the socket is dedicated to that particular machine and it does not draw >16A ( excepting start up).
I have come across this a few times.
It’s normally because people have had trouble with inrush currents for fork lift chargers.
My answer is normally
No I won’t do a 16A socket on a 20A ocd.
You can often provide 16A D type breaker instead
Or a 20A fixed connection.
[automerge]1601289951[/automerge]
How do you dedicate a socket to a particular machine?
In my experience, people will plug in what they want, where they want. Ignoring any labels or warnings if you put any up.
Appears to be ok according to the OSG, p190:
H3
Radial final circuits using 16 A socket-outlets complying with 85 EN 60309-2 (85 4343)
H3.1
General
Where a radial circuit feeds equipment the maximum demand of which, having allowed for diversity, is known or estimated not to exceed the rating of the overcurrent protective device and in any event does not exceed 20 A, the number of socket-outlets is unlimited.
H3.1
Circuit protection
The overcurrent protective device should have a rating not exceeding 20 A.
Except..... can't recall the reg number off the top of my head but ALL components in a chain require a rating to a minimum of the CPD, so in this case the 16a socket would need to have a rating of 20a minimum, which clearly it doesn't.
I came up on this issue on a scheme inspection years ago when I'd used a 10a rated switch that was switching something like 40w but it was being fed ultimately from a 13a fused outlet upstream that split.
Sorry for the grotty picture , but is this the reg you had in mind?
[ElectriciansForums.net] What do you think about a 16A socket on a 20A breaker
Or see if you've the Zs to fit a D type 16A (would be quicker and cheaper!)
Reply to What do you think about a 16A socket on a 20A breaker in the UK Electrical Forum area at ElectriciansForums.net
2 3