What earth system is this?? Pics attached | on ElectriciansForums
Discuss What earth system is this?? Pics attached in the Australia area at ElectriciansForums.net
srl-8
Morning,
I have attached a couple of pic's for you all to have a look at. I am finding it hard to know wether this is a TN-C-S or a TN-S.
Can anyone confirm. My thought is it is TN-C-S...
Thanks in advance. (still learning...~)
Srl-8
  • [ElectriciansForums.net] What earth system is this??  Pics attached
It is very hard to tell what you have there to be honest as you may find that the incomer cable is carrying an earth core with it.
There are several ways to check.
1. Call the DNO, this could be a fruitless exercise as the chances of you finding anyone to talk to that knows what your talking about is slim, but worth a try.
2. Take a Ze reading, if it's anything over 0.20 then chances are it is TN-S, but not always, but it can give you a guide.
3. Which will most likely be the best way to check is do a PSCC and PEFC test, if they are very close to same then it is TNC-S, if they are quite different then TN-S
My personal guess without doing the PSCC and PEFC test is TN-S just due to the age of the head.
:tounge_smile:Be sure bud but take a ZS reading first to be happy there is one
but if you are not sure dont worry get them in its a free service and its there issue depends is there any out buildings on the same supply
get them or remove the cover and a totall guess would you get continuity across them
but some one will tell us off sorry
good luck:tounge_smile:
That's a PME connection. You can clearly see the the neutral concentric part of the cable being taken to the neutral block. The only reason you can see this, is because there is no cable sealing chamber to this cut out arrangement.
That is Not a sheath earth, coming off the cable, look at it more carefully, and you can see the concentric arrangement.
Reply to What earth system is this?? Pics attached in the Australia area at ElectriciansForums.net
so Ze 0.35Ohms and my Part of the Circuit just half of R1+R2 is 0.19353Ohms as its 1.5mm x 10m so well under but dont know of any switch gear...
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...