Looks to be a TN-S conversion.

The original lead sheath may have corroded at a joint perhaps, and the DNO may then have opted to convert to TN-C-S rather than dig up the road to find the problem and repair it.

The braid yo see attached to the sheath is probably doing nothing more other than acting as a MPB to the incoming sheath of the supply cable.
 
There appears to be no seal on the cover, so if it was me I would have had a quick peek to see if there is a link between Neutral and Earth ;)

Other than that, testing would prove if similar readings are tested on pefc and pscc
 
Thats true, but a PME sticker and an earthing conductor connected to the neutral suggests that the installation is presented as TNC-S, a call to DNO/supplyer should confirm this if you have the will power.
 
If that is a DNO fix, it leaves a lot to be desired!! You don't mix TN-S and TNC-S. This is especially true in the case of a network supply cable, in the process of being converted to PME!! The TN-S sheath earthing clamp and braid should have been removed and any exposed LEAD sheath insulated with amalgamating tape!!!
 
If that is a DNO fix, it leaves a lot to be desired!! You don't mix TN-S and TNC-S. This is especially true in the case of a network supply cable, in the process of being converted to PME!! The TN-S sheath earthing clamp and braid should have been removed and any exposed LEAD sheath insulated with amalgamating tape!!!

Well you may be shocked to know this is standard procedure when fitting a new cutout on a paper lead cable.
How are you mixing TN-S and TNC-S? To carry this upgrade out the main must be PME and that was completed on the LV underground network in the 70's in my area so in doing that there was a mix.
Multiple new supplies to steel framed buildings can have a TN-S service made available from a PME main.
So I'm not sure why you have a problem with mixing systems if carried out correctly.
 
Well you may be shocked to know this is standard procedure when fitting a new cutout on a paper lead cable.
How are you mixing TN-S and TNC-S? To carry this upgrade out the main must be PME and that was completed on the LV underground network in the 70's in my area so in doing that there was a mix.

**Multiple new supplies to steel framed buildings can have a TN-S service made available from a PME main.
So I'm not sure why you have a problem with mixing systems
if carried out correctly.

Depends on what you are calling the ''Main''. Most underground networks are not yet fully PME'd, they are basically work in progress of becoming a true PME supply. There are not that many network distribution cables, that have been fully PME'd (every cable T joint PME'd) So, on most of these outgoing local network cables you will have both TN-S and TNC-S being supplied from the same cable. So why would you want to introduce the possibility of a neutral fault (however remote it may be) onto a presently sound TN-S section of the distribution cable?? Remembering also that many of the older domestic TN-S installations barely, or doesn't meet current earthing/bonding requirements at all!!

As far as i know, and as explained to me by a DNO area manager, when earthing the neutral at underground cable joints on cables that are supplying both TN-S and TNC-S at service heads, the original cable earthing is left maintained/continuous and forms no connection with the PME, N-E rodded connection.

It's fine to connect a service head as shown in the OP's photo, IF and only if the network distribution cable has been fully PME'd and that the installation connected to the service head is also PME compliant... Fine to mix TN-S with TT or TNC-S with TT, but it's not generally fine to mix TN systems together...

** If carried out correctly is the kicker isn't it, I take it you mean from previously TN-S distribution network cable that's been fully PME'd?? It's not going to happen, if all the other service heads on that supply cable have been connected as in the OP's example is it?? Other than that, i can't see how you can derive a TN-S supply from a TNC-S / PME cable, not unless you take a split concentric cable from a new joint and use earth rods to ground the earth conductor of that cable. Now that could be expensive to get below 0.80 ohms in the wrong soil conditions.
 
The LV main is the cable originating in the substation that all supplies will be breached from. it is run as a radial configuration sometimes with the option to be backfed or backfeed other LV mains via link disconnector boxes.
Any joint or repair carried out on a paper lead distribution cable will have neutral and earth connected together in that joint. They will already be connected at the substation and every main will have been PME'd at some point in the past. When a paper lead main or service is repaired wavecon CNE cable or hybrid will be used (3 core and copper neutral/earth 3 phase and 1 core and copper neutral/earth for single phase. On new supplies a rod must be installed every 40m (if there are joints) or before the last 4 properties on that main. This is to reduce the amount of customers affected by a neutral fault.
TN-S can be supplied from a PME'd main as previously mentioned, this is current practice on new installs with multiple supplies to steel framed buildings. This is to stop circulating currents in the frame. Alternatively no earth will be supplied and TT will most likely be used.
All the above is based on my knowledge of the DNO in my area and other areas may work to different practices.
 

Reply to What earthing system is this? in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
1K
  • Question
The issue I was having turned out to be a faulty transformer on the pole 30m away... after hassling the northern powergrid (and having then visit...
Replies
9
Views
771
We’ve recently completed the first and second fix of a barn conversion that is off grid with solar PV, batteries and a back up generator. This...
Replies
0
Views
198
  • Article
This is an RSS feed of thread: What are the best heating flushing systems Content of the thread: Any advice on selecting the best central heating...
Replies
0
Views
125
  • Question
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
Replies
5
Views
937

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks