Discuss What earthing system is this? in the Talk Electrician area at ElectriciansForums.net
where is it now?
where is it now?
Err... 42 Helmsome Rd, Leamington Spa, CV92 7DL:wink_smile:
Is that the cover with the sticker saying "earthing terminal PME system"?There appears to be no seal on the cover, so if it was me I would have had a quick peek to see if there is a link between Neutral and Earth
Other than that, testing would prove if similar readings are tested on pefc and pscc
If that is a DNO fix, it leaves a lot to be desired!! You don't mix TN-S and TNC-S. This is especially true in the case of a network supply cable, in the process of being converted to PME!! The TN-S sheath earthing clamp and braid should have been removed and any exposed LEAD sheath insulated with amalgamating tape!!!
Not heard of that before but some else may know.Does this also cure a noisy earth i heard, I might also be talking rubbish.
Well you may be shocked to know this is standard procedure when fitting a new cutout on a paper lead cable.
How are you mixing TN-S and TNC-S? To carry this upgrade out the main must be PME and that was completed on the LV underground network in the 70's in my area so in doing that there was a mix.
**Multiple new supplies to steel framed buildings can have a TN-S service made available from a PME main.
So I'm not sure why you have a problem with mixing systems if carried out correctly.