Defo a TN-S to TNC-S conversion, see them all the time in the Exeter area
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss What earthing system is this? in the Talk Electrician area at ElectriciansForums.net
If that is a DNO fix, it leaves a lot to be desired!! You don't mix TN-S and TNC-S. This is especially true in the case of a network supply cable, in the process of being converted to PME!! The TN-S sheath earthing clamp and braid should have been removed and any exposed LEAD sheath insulated with amalgamating tape!!!
Not heard of that before but some else may know.Does this also cure a noisy earth i heard, I might also be talking rubbish.
Well you may be shocked to know this is standard procedure when fitting a new cutout on a paper lead cable.
How are you mixing TN-S and TNC-S? To carry this upgrade out the main must be PME and that was completed on the LV underground network in the 70's in my area so in doing that there was a mix.
**Multiple new supplies to steel framed buildings can have a TN-S service made available from a PME main.
So I'm not sure why you have a problem with mixing systems if carried out correctly.
The LV main is the cable originating in the substation that all supplies will be breached from. it is run as a radial configuration sometimes with the option to be backfed or backfeed other LV mains via link disconnector boxes.
Any joint or repair carried out on a paper lead distribution cable will have neutral and earth connected together in that joint. They will already be connected at the substation and every main will have been PME'd at some point in the past. When a paper lead main or service is repaired wavecon CNE cable or hybrid will be used (3 core and copper neutral/earth 3 phase and 1 core and copper neutral/earth for single phase. On new supplies a rod must be installed every 40m (if there are joints) or before the last 4 properties on that main. This is to reduce the amount of customers affected by a neutral fault.
TN-S can be supplied from a PME'd main as previously mentioned, this is current practice on new installs with multiple supplies to steel framed buildings. This is to stop circulating currents in the frame. Alternatively no earth will be supplied and TT will most likely be used.
All the above is based on my knowledge of the DNO in my area and other areas may work to different practices.
I must admit, that I'm a bit confused here.
With TN-C-S, the supply is TN-C, which is presented at installations as TN-S.
To my mind, whether the TN-C is taken right up to the installation, or only taken to a point some distance away from the installation, It is still TN-C-S.
In either case, PME conditions will apply.
To my mind, the only way that a TN-C-S sytem can become TN-S, is for an isolating transformer to be used.
The TN-C would be fed to the transformer, and all feeds from the transformer would be TN-S.
Earthing the neutral at any point after the transformer, will effectivly re-establish the TN-C-S.
TN-S from CNE cable is achieved either by using split concentric service from main to cutout or CNE cable and a separate earth from the main joint to the cutout.
Neutral faults on the network are always a problem and the results can vary depending on system balance etc regardless of earthing arrangement.