I am never quite sure if I am doing too little or too much when someone has a flood and I am called in.

The most recent example is a chap has had fairly major flood damage to ceilings, carpets etc and it has poured through certain ceiling pendants and downlights.

Advice on the net states that a full EICR should be carried out. I feel this 'may' be too much and also not enough.

The chap has had some of his floorboards up, he can see where the flood water has gone and we can identify which lights are within the flood zone. Today I have pulled down every ceiling rose and downlight within the flood zone (which you wouldn't do with an EICR) to have a physical check and also carried out an IR test of the entire property to make sure nothing is sitting in water. Would you guys have done more than this? If so, what?

I haven't checked the loft, oven, garage (random examples of places/items definitely not affected by the flood) which you would do with an EICR but would be silly in this case.

PS.. I'm typing this on my new laptop... which I love! It has 8 core don't you know.
 
I would check that all exposed conductive parts on the affected circuits had R2 to them with the wander lead (and ideally every point in the flood zone, even where no ECPs present). Without confirming R2, you might get inaccurate IR results (for example, you had an unearthed class I light that had water sitting in it, it might not show up under an IR test if there was no earth continuity).

Also, would IR test between L+N combined, to the casing of any class II metal lights etc, again using the wander lead.

Other than that, I'd follow your approach.
 
I would check that all exposed conductive parts on the affected circuits had R2 to them with the wander lead (and ideally every point in the flood zone, even where no ECPs present). Without confirming R2, you might get inaccurate IR results (for example, you had an unearthed class I light that had water sitting in it, it might not show up under an IR test if there was no earth continuity).

Also, would IR test between L+N combined, to the casing of any class II metal lights etc, again using the wander lead.

Other than that, I'd follow your approach.
Really good point about the unearthed class 1. Luckily, I had only carried out an EICR on this same property a few months before, but that's besides the point and your point is a good one.
 
Whether things are directly in the flood area or not, the moisture in the air can corrode back boxes, electronics, switch contacts etc.

When my neighbours had a flood, everything was replaced except for lengths of cable…. Unless it was damaged itself by collapsing wet timber structures.

You don’t want to miss something out just because it wasn’t near the actual flood, just for it to become faulty a few months down the line.

Don’t start replacing anything until the dehumidifiers have done their work.
 

Reply to What electrical tests to do when someone has a flood? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
702
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
When I was at college doing the 2361 back in the 1980's I still recall to this day the instructor (Mr Wood) saying "Lads I do not want you to...
Replies
10
Views
518
Problems can arise when you get on too well then they think he won’t mind me doing a bit.
    • Friendly
    • Like
Replies
8
Views
539

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top