Hello,
I wanted to know what others would do with this situation.
Currently the house that I am going to rewire and replace CCU on has (starting at distributers cut out installed externally in box) from 60A fuse/service head are 16mm tails to meter, from meter 16mm tails to 100A DP isolating switch, from DP 10mm MICC to existing CCU approx 5 meters away.
Am going to replace the 10mm MICC with either either 16mm or 25mm SWA (max. current carrying capacity of 10mm PVC sleaved MICC clipped dircet =77A)
As the tails from DP to CCU are over 3m in length, I have to install a SP&N switchfuse within the first 3 meters. I will prob. remove DP isolator in external box and put switchfuse in there if there is room and ownership of box cannot be 100% established.
So finally to my question - if the distributers cut out is 60A what rated fuse would you put in the switchfuse?
All suggestions welcome.
Thanks.
I wanted to know what others would do with this situation.
Currently the house that I am going to rewire and replace CCU on has (starting at distributers cut out installed externally in box) from 60A fuse/service head are 16mm tails to meter, from meter 16mm tails to 100A DP isolating switch, from DP 10mm MICC to existing CCU approx 5 meters away.
Am going to replace the 10mm MICC with either either 16mm or 25mm SWA (max. current carrying capacity of 10mm PVC sleaved MICC clipped dircet =77A)
As the tails from DP to CCU are over 3m in length, I have to install a SP&N switchfuse within the first 3 meters. I will prob. remove DP isolator in external box and put switchfuse in there if there is room and ownership of box cannot be 100% established.
So finally to my question - if the distributers cut out is 60A what rated fuse would you put in the switchfuse?
All suggestions welcome.
Thanks.